APC SM1000c to SE M340 modbus TCP comms

kuckphoto

Member
Join Date
Nov 2018
Location
Kentucky
Posts
5
Hi has any one linked a Schneider Electric Smart UPS to a PLC through Modbus TCP? Supposedly it can do it, I'm told. but I'm not entirely sure how. I know the modbus addresses that I want to bring into the PLC but being fairly new to Schneider and Modbus I don't know how to proceed.

We're using a BMXP342020 and a SMT1000C

Any help or a point in the right direction would be greatly appreciated.
 
Since you don't have a NOC or NOE comms card in the PLC rack, you'll have to do this using READ_VAR function block in the PLC through the processor ethernet port.

Its a challenge getting it working the first time...

Do a search for READ_VAR on this forum, there was a chap recently trying to do something very similar, but to some red lion remote I/O.
 
Timeout GEST

The timeout value in the GEST control block should be set to a nonzero value using a MOVE before you hit the read_var the first time. It looks at the timeout when it starts the communication. Zero corresponds to an infinite timeout. If there is a zero in that GEST element and your read_var is not successful it will probably hang up and you will have to cycle power on the processor. Loading a nonzero value after the fact will not recover the read_var.

Triggering the read_var seems to not be very well documented if you don't want it to go continuously. Too many Read_vars going at one time may lead to socket count problems. Expose the EN pin on the block and one-shot it whenever your want a communication to start. When I've had several read_vars that need to be sequentially triggered I've used SFC to sequence them.

I'm not sure where the term 'GEST' came from. I suspect it's an abbreviation for something in French.

Read_var is subject to the usual Modbus issues with address offset versus communications index. The result is that you may have to adjust your register number up or down by 1 to get the correct data.

Older Modicon software could not put the return of a communications command into an 'unlocated' variable. It had to go into register space. Now you have the better option to go into an unlocated. You will have to turn a project option to allow dynamic array indexing - I forget the exact term for the option.

I wish you well with your project.
 

Similar Topics

This is a program in a machine that has been running for about 7 years without any issue like this. We have a master servo (the machine's main...
Replies
3
Views
1,158
If f.i. the slave axis has to start the camming not from the beginning of the cam but somewhere in between, the parameter 'cam lock position' has...
Replies
0
Views
1,402
In a Siemens controller when I have a cam where f.i. master- and slave position is absolute, when the the camming is started the slave will first...
Replies
0
Views
1,584
Please tell me how to correct two alarms on APC Galaxy 3000 UPS: #1: Cooling fault (Cooling liquid level is low) #2: End of batt service life Due...
Replies
2
Views
1,414
Good Morning , I'm having a problem with a Kinetix Servo MAPC instruction. I keep getting a #85 Fault. Could you give me some...
Replies
1
Views
1,656
Back