This is a continuation of a thread that I started a few weeks ago at the now defunct RSI forum. It was a 3-way conversation there between Ken Roach, Andy123(ContrConn?), and myself. A brief summary follows. Any ethernet experts hanging out here - feel free to jump in.
The problem is with a CLX system installed in 2003 that uses ethernet for I/O. The attached IOCfg.zip file contains a .jpg file showing the I/O tree. As you can see, the I/O is divided between two ENBT's. The attached .pdf files are relevant to the ENBT in slot 9.
Approximately 14 months after installation, comms failed to one of the flex I/O groups causing a small fire. Subsequently, some monitoring programming was installed using GSV instructions to monitor "entry status" of every module in the system. This programming is detecting multiple, frequent errors on all of the flex I/O groups - predominantly on the groups under the ENBT in slot 9. When a fault occurs, the "entry status" for each of the I/O modules goes bad at the same time but the adapter status remains good. The duration of the fault is approx. 8 seconds. The fault code from each of the modules is hex 0203 indicating a lost connection. In spite of the errors, the line continues to run. There are rare occasions, however, when the error does not clear.
There was some questioning of how often the GSV's should be executed - i.e. am I creating the errors?
It was recommended to upgrade the ENBT firmware to 3.9 - has been done - no change.
All ethernet connections are to a Hirschmann 'Mice' switch.
Just before we were cut off at RSI, there was talk of analysing the system with 'ethereal'. I have that program and have even fired it up a few times - but I don't really know what I'm looking at there.
The problem is with a CLX system installed in 2003 that uses ethernet for I/O. The attached IOCfg.zip file contains a .jpg file showing the I/O tree. As you can see, the I/O is divided between two ENBT's. The attached .pdf files are relevant to the ENBT in slot 9.
Approximately 14 months after installation, comms failed to one of the flex I/O groups causing a small fire. Subsequently, some monitoring programming was installed using GSV instructions to monitor "entry status" of every module in the system. This programming is detecting multiple, frequent errors on all of the flex I/O groups - predominantly on the groups under the ENBT in slot 9. When a fault occurs, the "entry status" for each of the I/O modules goes bad at the same time but the adapter status remains good. The duration of the fault is approx. 8 seconds. The fault code from each of the modules is hex 0203 indicating a lost connection. In spite of the errors, the line continues to run. There are rare occasions, however, when the error does not clear.
There was some questioning of how often the GSV's should be executed - i.e. am I creating the errors?
It was recommended to upgrade the ENBT firmware to 3.9 - has been done - no change.
All ethernet connections are to a Hirschmann 'Mice' switch.
Just before we were cut off at RSI, there was talk of analysing the system with 'ethereal'. I have that program and have even fired it up a few times - but I don't really know what I'm looking at there.