Title says it all. I've loaded up my program on the emulator, but when I open up FactoryTalk View ME Station, RsLogix goes offline with the following error:

"Can't communicate with Linx communication software. Logix Designer has been taken offline. If online operations are in progress, they will not be completed. Offline operations after communication loss will result in loss of correlation. To avoi dloss of correlation, close views without applying changes before attempting to go online. Error 806-80042535"

When I go to "Who Active," to reconnect, I get the following error:

"FactoryTalk Linx(localhost) is not started or started with error, please check FactoryTalk Linx and restart Network Browser."

I've restarted the "FactoryTalk Linx Broswer UI" service, which hasn't fixed the problem. I know the emulator is still working correctly, because I'm able to write values to it from an OPC server, and I can see them changing in station. I just can't view the running logic in Logix.

What I've found is that the issue is order of operations. If I open up station first, then I have no issue connecting with Logix.

Has anyone else experienced this issue? Is this normal? Did I screw up a communication setting somewhere?

Many Thanks for the help,
Hunter
 
I'm wondering if you have a conflict in Emulate with FactoryTalk Linx and RSLinx Classic "modules" maybe using the same virtual slot. Just a guess. I usually configure RSLinx Classic to use slot 16 and FactoryTalk Linx to use slot #15. FT Linx has an auto-configure option that I disable when I set it to slot #15.

I assume you are using Ethernet for communications. Do you have Logix 5000 software setup to use RSLinx Classic or FT Linx?

OG
 

Similar Topics

Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
138
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
568
Is there a way to use the FAL instruction to do +=2 instead of +=1? I have an array that is organized with alternating "data" and "flag" values...
Replies
5
Views
125
I have an AOI with revision notes. Someone entered the last note into the description instead of the notes. I cannot just click into the revision...
Replies
4
Views
148
Back
Top Bottom