Asking for communication betwwen Micro 850 (CCW) and Danfoss FC 102 VFD ( Modbus RTU)
hoainam2310
Oct 2019
canada
Hi everyone,
I would like to use Micro 850 to control DF FC 102. I adready connect Danfoss fc 102 VFD ( it can run the motor) to Micro 850 by embedded sirial port. and set the controller - Sirial port: Modbus RTU - RS485. (picture 2)
I dlready write the testing program (picture 3), and set the LocalCfg and TagetCfg ( picture 4 &5)
According to Danfoss modbus manual, i found the modbus address to read Frequency is 16129 ( picture 1) .
I already tried a lot of Modbus Addresses like 16130, 416129, 416130 ( for Frequency) and 16139, 16140, 416139, 416140 ( for current). But the value I recieved from Modbus LocalAds is always 0. ( the VFD was controlling the motor at that time, the motor was running).
I am new in CCW; therefore, I do not know what I did wrong. i watched a lot of Tim Wiborne's videos but still do not know how to solve it as well.
If anyone has the answer please let me know. I really appriciate it.
This will work 100%!
Hello friend,
I promise you this solution will work 100%. All you need to do is switch the white and black wires on your Modbus Adaptor. Therefore your problem is a polarity issue.
Cheers!👨🏻‍🏫
hello everyone, I have 2 PLCs controller : Micro850, and 1 HMI PV800. I use CCW to write the program. I already finished programing for both PLCs...
1,436
Happy Friday, I am trying to log scan errors related to Modbus Comms for a G306. I am able to use the system function GetDeviceStatus(x) to...
1,923
Getting a trend of the control output, target position and actual position is a must. For a velocity control application substitute velocity for...
2,328
I am trying to create a network setup that would take many devices that are working together and have them appear as one device or IP on a network...
2,278
Hello, How can I set Studio 5000 to use licenses from Local Folder, not network folder? I'm using Studio 5000 30.00. Computer has all licenses...
4,907