Old April 7th, 2021, 05:40 AM   #1
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Can't connect anymore [CP1L]

Hello everybody,

I'm using a Cp1l-EM40 PLC for my projects and this morning I changed the PLC IP from 192.168.250.2 to 169.254.67.1, because I needed to test something... My laptops IP is 169.254.67.105, so it should have been in the correct range. However, I can't connect to my PLC anymore. CX-programmer gives the error: Failed to connect to the PLC. Is there a way to change the IP back to 192.168.250.2?

Thanks!
Olivier
  Reply With Quote
Old April 7th, 2021, 06:28 AM   #2
Wasan
Member
Thailand

Wasan is offline
 
Wasan's Avatar
 
Join Date: Jun 2015
Location: Bangkok
Posts: 75
Quote:
Originally Posted by olivier_vl View Post
Hello everybody,

I'm using a Cp1l-EM40 PLC for my projects and this morning I changed the PLC IP from 192.168.250.2 to 169.254.67.1, because I needed to test something... My laptops IP is 169.254.67.105, so it should have been in the correct range. However, I can't connect to my PLC anymore. CX-programmer gives the error: Failed to connect to the PLC. Is there a way to change the IP back to 192.168.250.2?

Thanks!
Olivier
Maybe this link help you by use direct connection with your PLC.

https://www.myomron.com/index.php?ac...b&article=1487
__________________
Wasan Thawon

My Blog: https://scadaskill.blogspot.com/

Facebook Page: https://www.facebook.com/scadaskill

Youtube Channel: https://www.youtube.com/scadaskill
  Reply With Quote
Old April 7th, 2021, 06:56 AM   #3
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Quote:
Originally Posted by Wasan View Post
Maybe this link help you by use direct connection with your PLC.

https://www.myomron.com/index.php?ac...b&article=1487
Thanks, but i have already tried that and it didn't work.

This is by the way the window I get when I start DirectEthernetUtility.
Attached Images
File Type: png DirectEthernetUtility.png (20.4 KB, 41 views)
  Reply With Quote
Old April 7th, 2021, 07:52 AM   #4
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,662
what is the netmask of the PC?
  Reply With Quote
Old April 7th, 2021, 08:01 AM   #5
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Quote:
Originally Posted by drbitboy View Post
what is the netmask of the PC?
Ethernet adapter Ethernet:

IPv4 Address. . . . . . . . . . . : 169.254.67.105
Subnet Mask . . . . . . . . . . . : 255.255.0.0
Default Gateway . . . . . . . . . : 192.168.250.255

If this is what you meant with (sub)netmask
  Reply With Quote
Old April 7th, 2021, 08:11 AM   #6
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,662
Quote:
Originally Posted by olivier_vl View Post
Ethernet adapter Ethernet:

IPv4 Address. . . . . . . . . . . : 169.254.67.105
Subnet Mask . . . . . . . . . . . : 255.255.0.0
Default Gateway . . . . . . . . . : 192.168.250.255

If this is what you meant with (sub)netmask

Yes, and that subnet mask should work. You could try 255.255.255.0, or whatever the PLC was set to be, but it should make no difference.



That default gateway is mis-configured; it should not matter for the current effort, but change it to 169.254.1.1 for sanity's sake.


Do you have access to Wireshark or tcpdump? If the PLC is sending out any ARP or other broadcast packets, you should be able to double-check its IP address.




Try another cable.


Try putting a switch that does auto-negotiation in between the PC and the PLC (requires two cables); perhaps neither side is doing auto-negotiation for the cable pinouts.

Last edited by drbitboy; April 7th, 2021 at 08:18 AM.
  Reply With Quote
Old April 7th, 2021, 08:26 AM   #7
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 624
Quote:
Originally Posted by olivier_vl View Post
Ethernet adapter Ethernet:

IPv4 Address. . . . . . . . . . . : 169.254.67.105
Subnet Mask . . . . . . . . . . . : 255.255.0.0
Default Gateway . . . . . . . . . : 192.168.250.255

If this is what you meant with (sub)netmask
Using a 255.255.255.0 is more efficient than 255.255.0.0 , but then the gateway ended with .255 is wrong since the last IP is reserved, it's the broadcast address.

You can also try a port scanner, this works quite well, it can be run without installing it https://www.advanced-port-scanner.com/
__________________
Suppanel HMI
  Reply With Quote
Old April 7th, 2021, 08:52 AM   #8
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Quote:
Originally Posted by drbitboy View Post
Yes, and that subnet mask should work. You could try 255.255.255.0, or whatever the PLC was set to be, but it should make no difference.



That default gateway is mis-configured; it should not matter for the current effort, but change it to 169.254.1.1 for sanity's sake.


Do you have access to Wireshark or tcpdump? If the PLC is sending out any ARP or other broadcast packets, you should be able to double-check its IP address.




Try another cable.


Try putting a switch that does auto-negotiation in between the PC and the PLC (requires two cables); perhaps neither side is doing auto-negotiation for the cable pinouts.

That's the 'standard' IP-address. But I dont have Wireshark/tcpdump installed on this laptop, but i will do that the next workday. I have tried another cable already.

Quote:
Originally Posted by lfe View Post
Using a 255.255.255.0 is more efficient than 255.255.0.0 , but then the gateway ended with .255 is wrong since the last IP is reserved, it's the broadcast address.

You can also try a port scanner, this works quite well, it can be run without installing it https://www.advanced-port-scanner.com/
It didn't find any active or inactive networks, so that's weird

Last edited by olivier_vl; April 7th, 2021 at 09:00 AM.
  Reply With Quote
Old April 7th, 2021, 09:00 AM   #9
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,454
Quote:
Originally Posted by olivier_vl
this morning I changed the PLC IP from 192.168.250.2 to 169.254.67.1
What are the odds that there was a device that was/is using that IP address of 169.254.67.1 and now you have two devices with the same address?

Try unplugging the PLC and PING 169.254.67.1 to see if you get a response
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old April 7th, 2021, 09:19 AM   #10
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Quote:
Originally Posted by geniusintraining View Post
What are the odds that there was a device that was/is using that IP address of 169.254.67.1 and now you have two devices with the same address?

Try unplugging the PLC and PING 169.254.67.1 to see if you get a response
Hmm I would be very surprised if there's another device that is using the same IP address.

When I ping 169.254.67.1:
Ping statistics for 169.254.67.1:
Packets: Sent = 4, Received = 4, Lost = 0 (0% loss)
  Reply With Quote
Old April 7th, 2021, 09:22 AM   #11
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,454
Is that with the PLC plugged in ? unplug the Ethernet cable from the PLC and try it... if you get a response 0% loss then you have another device with the same address and you need to unplug it and change the PLC or use a serial/USB cable to change the PLC
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old April 7th, 2021, 01:18 PM   #12
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Quote:
Originally Posted by geniusintraining View Post
Is that with the PLC plugged in ? unplug the Ethernet cable from the PLC and try it... if you get a response 0% loss then you have another device with the same address and you need to unplug it and change the PLC or use a serial/USB cable to change the PLC
Oh yeah, I'm sorry that was with the PLC plugged in. I tried it with the PLC unplugged and these are the results:

Ping statistics for 169.254.67.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
  Reply With Quote
Old April 7th, 2021, 02:08 PM   #13
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,454
Perfect, we now know its the only one on the network, I would try the settings below on your PC

IPv4 Address. . . . . . . . . . . : 169.254.67.105
Subnet Mask . . . . . . . . . . . : 255.255.255.0
Default Gateway . . . . . . . . . : 192.168.250.1

If that does not work, do you have a USB cable? then you can go into the PLC via USB and make the changes
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old April 8th, 2021, 03:23 AM   #14
olivier_vl
Member
Netherlands

olivier_vl is offline
 
Join Date: Apr 2021
Location: Zuid-Holland
Posts: 7
Quote:
Originally Posted by geniusintraining View Post
Perfect, we now know its the only one on the network, I would try the settings below on your PC

IPv4 Address. . . . . . . . . . . : 169.254.67.105
Subnet Mask . . . . . . . . . . . : 255.255.255.0
Default Gateway . . . . . . . . . : 192.168.250.1

If that does not work, do you have a USB cable? then you can go into the PLC via USB and make the changes
I tried those settings, but they didn't work either. I currently don't have an USB cable, because they are at the company itself and I'm working from home... So I think I need to make a ride to get the USB cable.

EDIT: I just tried some other stuff with auto negotation and I was surprised but i was able to connect to the plc!! So thanks!!

Last edited by olivier_vl; April 8th, 2021 at 03:27 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1734-AENT will connect Drew Ethridge LIVE PLC Questions And Answers 12 January 7th, 2021 10:19 AM
HMI can connect to PC over ethernet directly, but not a switch or PLC novice_user111 LIVE PLC Questions And Answers 10 April 5th, 2019 04:13 AM
Setting up OPC server for a SLC500, won't connect with RSlogix OPC Test BigTom209 LIVE PLC Questions And Answers 9 March 22nd, 2010 11:06 AM
Starter connect to mm440 by tcp/ip dis LIVE PLC Questions And Answers 10 January 19th, 2010 10:07 PM
Connect laptop > ML1000 problem Martindag LIVE PLC Questions And Answers 8 October 1st, 2009 09:58 PM


All times are GMT -4. The time now is 10:41 AM.


.