Problem with air compressor

Hello friends

I have new project

Air compressor the company want to upgrade it to work with PLC and HMI

The compressor work with micro processor and the micro processor

Is damaged the problem in 2 solenoid open the air gate and if the solenoid coil is broken the micro processor stop the machine and make alarm

The solenoid coil is normal only 2 wire 24v dc

How the micro processor feel the broken coil and if the wire is cut

And the owner need in the upgrade this feature

How can I make the plc feel the coil if broken or damaged

I will use plc s7 200 with out put relay

I think the micro processor measure the coil resistance

But in the plc ? what we will use ?

Sorry about my little English

And I am wait to answers me
__________________
elhagan ( egypt )
i will be happy if you understand me
i will be good if you learn me
i will be blissful if you make me your friend
  Reply With Quote
Old January 26th, 2006, 12:15 PM   #2
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,152
Some PLCs manufacturers have output cards that will detect an open circuit on the output. I have only seen this feature with solid state outputs, never with relay outputs. The PLC output circuit applies a very low voltage limited current to the output terminal. This signal is not strong enough to activate a solenoid coil but it indicates to the controller if there is a completed circuit.
  Reply With Quote
Old January 26th, 2006, 01:05 PM   #3
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 2,033
Wire the output as sinking. Wire an input directly to the output.
Input will be on when output is off, if the coil has continuity.
Input will be off when output is on.
  Reply With Quote
Old January 26th, 2006, 01:17 PM   #4
10baseT
Member
United Kingdom

10baseT is offline
 
Join Date: Nov 2005
Location: wrexham
Posts: 271
You could also play the same trick with the input - have it high all the time , and the coil will pull it down . Touble is , that even if the coil fails , there is a chance that leakage alone will be enough to give spurious inputs . How about using a change over relay (actually not necessary) , and wacking a voltage over the coil with a ballast resistor (high impedance), you could then use an analogue voltage input to measure the voltage across the coil , which would change if the coil failed .
  Reply With Quote
Old January 26th, 2006, 01:18 PM   #5
stasis
Member
United States

stasis is offline
 
Join Date: Mar 2005
Location: Columbus, Ga
Posts: 344
an alternate method would be to use a pressure switch tied to a timer. If in X time the pressure switch doesn't activate/deactivate...
  Reply With Quote
Old January 26th, 2006, 01:53 PM   #6
10baseT
Member
United Kingdom

10baseT is offline
 
Join Date: Nov 2005
Location: wrexham
Posts: 271
Like that one even better stasis , now that is the proper way to go .
  Reply With Quote
Old January 26th, 2006, 04:15 PM   #7
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,152
Try a current sensing relay:

http://www.newarkinone.com/NewarkWeb...KU=90F3320&N=0

or a leakage monitoring relay
http://library.abb.com/GLOBAL/SCOT/S...04C0203_02.pdf
  Reply With Quote
Old January 26th, 2006, 07:30 PM   #8
elhagan
Member
Egypt

elhagan is offline
 
elhagan's Avatar
 
Join Date: Sep 2003
Location: cairo
Posts: 48
dear Alaric

thank you very much can you tell me what the kind for this plc

and any mark and i see current sensing and leakage monitoring relay

its very good from you this is what i need but if i found the good plc will detect an open circuit on the output its will be the good idea i wait for your replay i need the plc manufacturers

and data sheet about it


dear keithkyll

i cant understand who is the input i have one solnied and need to feel it if the coil is damaged or broken the machine will stop


dear 10baseT

thank you for your help


dear stasis

big story to use pressure switch tied to a timer stasis another circle man

__________________
elhagan ( egypt )
i will be happy if you understand me
i will be good if you learn me
i will be blissful if you make me your friend

Last edited by elhagan; January 26th, 2006 at 07:32 PM.
  Reply With Quote
Old January 27th, 2006, 04:39 AM   #9
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 2,033
Output is relay. Solenoid has +24DC. Relay is controlling the zero side of the solenoid.

Think backwards. When the relay is off, +24 volts will pass through the solenoid coil to the relay contact. Connect a PLC input to this point.
I assume input is on with 24 DC input - off with zero.

If the PLC input has a 4ma load, then there will always be 4ma on the solenoid. This shouldn't be a problem, unless the solenoid is very small.
  Reply With Quote
Old January 27th, 2006, 06:53 AM   #10
elhagan
Member
Egypt

elhagan is offline
 
elhagan's Avatar
 
Join Date: Sep 2003
Location: cairo
Posts: 48
Thumbs up

Quote:
Originally Posted by keithkyll
Output is relay. Solenoid has +24DC. Relay is controlling the zero side of the solenoid.

Think backwards. When the relay is off, +24 volts will pass through the solenoid coil to the relay contact. Connect a PLC input to this point.
I assume input is on with 24 DC input - off with zero.

If the PLC input has a 4ma load, then there will always be 4ma on the solenoid. This shouldn't be a problem, unless the solenoid is very small.
dear keithkyll
can you draw this steps for me
__________________
elhagan ( egypt )
i will be happy if you understand me
i will be good if you learn me
i will be blissful if you make me your friend
  Reply With Quote
Old January 27th, 2006, 07:16 AM   #11
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 2,033
Wire the output normally. Add a jumper from the output terminal to an input terminal.
Someone help me out here with a drawing.

elhagen, think of using a meter to troubleshoot the output. Red lead on Output terminal, black lead on ground. When the output is on, meter will read zero volts. When the output is off, meter will read 24 volts if the solenoid is not open. If the solenoid is open, you will always read zero volts.

Use a PLC input as a meter.

Last edited by keithkyll; January 27th, 2006 at 07:26 AM. Reason: More info
  Reply With Quote
Old January 27th, 2006, 09:47 AM   #12
Kidblue
Lifetime Supporting Member
England

Kidblue is offline
 
Kidblue's Avatar
 
Join Date: May 2003
Location: Worcester
Posts: 698
Hope the attached sketch helps.....

Regards


Rob.
Attached Files
File Type: pdf Current Sense.pdf (7.3 KB, 45 views)
__________________
Rob Howdle

.........For the Boys in Royal Blue !!
  Reply With Quote
Old January 28th, 2006, 07:24 AM   #13
elhagan
Member
Egypt

elhagan is offline
 
elhagan's Avatar
 
Join Date: Sep 2003
Location: cairo
Posts: 48
dear sir Alaric
can you answer me please
__________________
elhagan ( egypt )
i will be happy if you understand me
i will be good if you learn me
i will be blissful if you make me your friend
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Boiler Fuel Feed Simulation for Bunker C sjknight LIVE PLC Questions And Answers 1 November 20th, 2005 05:42 PM
S7 - just for info, curious problem with Labels RMA LIVE PLC Questions And Answers 1 June 29th, 2005 02:02 PM
Flowmeter for compressor control (compressed air) LittleOne LIVE PLC Questions And Answers 19 March 9th, 2005 07:51 PM
Ab Plc5 Rio Problem. fernandes LIVE PLC Questions And Answers 5 March 7th, 2004 02:25 PM
PLC5/40 Backplane Problem????? Andrew Evenson LIVE PLC Questions And Answers 18 August 24th, 2002 08:06 PM


All times are GMT -4. The time now is 02:14 PM.


.