Connecting OP27 to PC
girevik
Nov 2005
rus
179
Hello,
i'm trying to connect Simatic OP27 Panel to the PC.
I have a USB/MPI adapter, which request 24V power supply, as i have read, OP does not have such power supply, so i'm unable to use that adapter with OP27, right? (btw, would external power supply fix the problem)?
I also have rs232 cable, but i'm not sure I can use that since there is a rs422/485 label on the OP, so that way (without 485/232 adapter) would not work i believe, is that right?
I also have read that I should use IF2 (rs232/TTY port) to connect op27 to PC, but i'm not sure how I it's possible - that port looks strange. However i have found pins diagramm for that port, so i'm wondering if I can just connect rs232 cable to those pins (i.e. use home-made adapter)?
thanks
parky said:
It is ok to use 232 that's how you normaly program them.
thanks for your reply.
Do you mean that 232 on the op27 which looks like a standard rs232 on PC (9 pin, marked as 422/485) or that IF2 (15 pin, marked rs232, tty)?
thanks
which one of those two?
thanks!
If my memory serves me right, it's the 15 pin, I have a siemens lead for the OP range but it is at work.
When I go back after my holiday I will check it out & confirm.
Parky,
Thank you for your help!!
I guess too that 15 pin is the right choice, I will probably try that tomorrow...
thanks again
parky,
I have tried to make a cable IF2(15 pin) to 9-pin rs232 (PC side) but it wont work. There is something wrong with the cable. I have used OP27 manual but probably I have misunderstood something.
If you do have that cable, could you give me the pinout? so i would be able to make the cable.
thanks
thank you for your reply, JesperMP,
the picture does not work, could you try again?
btw i have tried to find that cable in the CA01, but have found 6XV1440-2K... only. I guess that is what i need.
thanks!
JesperMP,
I also have found your old post:
The cable type # is: 6XV1440-2KH32
On the 15-pin OP plug is noted: "TD/OP V.24". Insert in IF2 port on the OP.
On the 9-pin PC plug is noted: "TI505/PC V.24". Insert in serial port on the PC.
Do it yourself description:
OP plug: PC plug:
15-pin male 9-pin female
pin 1 shield ------ pin 1 shield
pin 3 RxD ------ pin 3 TxD
pin 4 TxD ------ pin 2 RxD
pin 12 Gnd ------ pin 5 Gnd
pin 1-6-4 jumper
pin 7-8 jumper
Notice: This is for a standard 9-pin serial port in a standard PC.
If you have a Siemens PG, then the cable is not the same.
I think that's what I need.
thanks
We have a client who wants to connect a Siemens OP27 HMI to his OMRON CJ1M-CPU11 via RS232. Would anyone be able to point me to a cable pinout to...
6,420
I have 2 PLCs. One is networked to our plant, and the other is networked to the first PLC via a 1756-EN2T. I could easily get the second PLC...
57
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
64
102
Hello, I was looking to store some values from our FactoryTalk Application using Datalog to a MariaDB. I see there is quite a bit of documentation...
119