Simotion Scout Fault: F07411
emfennell
Feb 2011
Nashville, TN
Does anyone have any information on this Simotion Fault F07411 which is a Drive Fault Flux Controller Output Limited? I cannot figure out what is triggering this fault or how to correct it for happenning again.
The help function for Simotion Scout is the worse I've seen yet so far!
Is this the help you get ?
Code:
F07411
Drive: Flux controller output limited
Reaction:
OFF2 (NONE, OFF1)
Acknowledge:
IMMEDIATELY
Cause:
The specified flux setpoint cannot be reached although 90% of the maximum current has been specified.
- incorrect motor data.
- motor data and motor configuration (star/delta) do not match.
- the current limit has been set too low for the motor.
- induction motor (sensorless, open-loop controlled) in I2t limiting.
- the Motor Module is too small.
Remedy:
- correct the motor data.
- check the motor configuration.
- correct the current limits (p0640, p0323).
- reduce the induction motor load.
- if required, use a larger Motor Module.
Yes, I verified that in operation its not reaching its current limit or its torque limit. The is still good (same as when working correctly) and the load for our application has not changed. So basically everything that the help file told me to checked has been verified.
Hello, I am new to Siemens' Simotion Scout software. I looked for a thread that might include this but...I have a CU320 and an existing project...
2,639
Dear, I have using simotion drive for motion control. I have less experience in d425. So I have so questions about about that please give...
4,125
Hello All, I need change some on Simotion Scout project. (change referance, cancel some drive etc..) I need help. Sure not free. Crb_n
2,596
plc SIMOTION D425 MODEL: 6AU1425-0AA00-0AA0 you help me could you help me for a links ? fix I can download software simotion Scout D425 model...
1,638
Does anyone have experience with the Hilsher NL50-MPI Ethernet to Profibus adapter with Simotion Scout? I am using VMWare to run Windows XP with...
3,780