Powerflex 525 Fault code F013 ground fault
unsaint32
Oct 2012
minneapolis
365
At my work, a coil of plastic tubing goes over retracted circular fingers. A Poweflex 525 drives a motor to extend the fingers open to hold the coil, to be shrink wrapped. But only when it's time to retract the fingers, the 525 faults with the code; "F013 Ground Fault."
Before I look at the motor wiring, I wanted to get some opinions as to why the vfd faults only in one direction?
I just checked the voltage at u, v, w terminals to ground, and they were all 2.3volts (I did not reset the fault). If there really was a grnd fault, would I not get 0V on at least one of the three terminals?
There's a known anomaly with ground faults on 230V 3PH Frame A or B PF525 drives manufactured before Aug 1 2013. If your drive fits this description you might want to check the drives manufactured date. I assume from the article that this is an inherent problem and most likely the drive, or a part therein will have to be replaced.
562950 - PowerFlex 525 3 Phase 230V AC: Having an intermittently F013 Ground Fault
Access Level: Everyone
Regards,
George
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
63
So our Powerflex 525's are set up to allow REMOTE operation from PLC through network. But if network is lost we want to be able to run in LOCAL...
575
I recognize that I need to factory reset the drive and that P053 is my ticket. Problem statement: I can't get passed the fault display to get to...
1,473
I am getting a motor stalled fault on a VFD for a incline conveyor motor with a electric brake. I notice that when the VFD is supposed to ramp...
4,276
We have a powerflex 525 VFD and today got a F012 Fault on it which is HW over current. I am not really sure what a Hardware Overcurrent fault is...
3,117