charlesG123
Member
Hello,
I have a 1734-AENT POINT I/O with 1734-IE2V in it and I have noticed that the accuracy of the value is low at low voltage. For example when I send 874mV, the PLC reads anywhere between 840 and 910 and it keeps changing even tho the 874mV I'm sending is stable. that is almost a 5% change in the value. If i send a higher voltage like for example 1.75V, the plc reads 1745 to 1755 which is about 1% precision which is much better. All of my IE2V does the same, I was wondering if this was a normal behavior or if something was wrong with my POINT I/O?
Thanks.
I have a 1734-AENT POINT I/O with 1734-IE2V in it and I have noticed that the accuracy of the value is low at low voltage. For example when I send 874mV, the PLC reads anywhere between 840 and 910 and it keeps changing even tho the 874mV I'm sending is stable. that is almost a 5% change in the value. If i send a higher voltage like for example 1.75V, the plc reads 1745 to 1755 which is about 1% precision which is much better. All of my IE2V does the same, I was wondering if this was a normal behavior or if something was wrong with my POINT I/O?
Thanks.