Prosoft Communication

VarunM

Member
Join Date
Nov 2024
Location
New Jersey
Posts
4
Hi all, I have a A4 chassis to use with 1756-L81E and MVI56E-MNETC Prosoft module. Slot 0 is 1756-L81E, and Slot 1 is MVI56E-MNETC.

I am currently trying to communicate with modsim-64 trial version installed in my PC. I Believe I have done configuring the ProSoft correctly. Connected and downloaded the Prosoft builder file into it. Both my processor and ProSoft module seems to be fine looking at the module status. RSLinx looks fine as well. I could see these two modules online.

Add on instruction is imported to my ladder logic from ProSoft website. But still can't read or write data from controller tags to modsim-64 or vice versa.
 
As I recall there is an enable bit that needs to be set in the MNETC.
Have you connected using the builder software and viewed the module status in realtime? There might be some answers there.
I have one running a few feet away so if you need a specific thing looked at I can connect and look.
 
As I recall there is an enable bit that needs to be set in the MNETC.
Have you connected using the builder software and viewed the module status in realtime? There might be some answers there.
I have one running a few feet away so if you need a specific thing looked at I can connect and look.

Second this. I haven't used this particular ProSoft module, but the Profibus version requires logic to set an enable to communicate.
 

Similar Topics

Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
1
Views
418
We have two sites that are stranded with no line of site, they are handled by phone/modem with a chain that includes: Stranded site (client)...
Replies
5
Views
1,175
Does anyone have experience with setting up a HC900 to a prosoft card? Using this to communicate with an Allen Bradley plc
Replies
1
Views
987
I am using modbus communication module MVI56E-MCMR in communicating with another PLC(my plc is Master) and DCS(my plc is Slave). I am asking if it...
Replies
2
Views
1,538
Can someone help me? I'm using Studio5000 to build a project in v21. All samples of ProSoft regarding MVI94-MCM communication and configuration...
Replies
3
Views
3,742
Back
Top Bottom