SLC 5/05 1747-L551C ethernet communications to ABB VFD
I did review the different communication modes, but considering I only want to get speed, power, and flow for now, I think just doing the 3 EEM should be okay. I'll probably only run the EEM routine every few seconds, too.
Okay, communications is working, but not getting the data that I think it should be. I think it should be a value of 0 (vfd is not currently running) in data table N17:0
Any suggestions? I've used different commands and service codes than the scant examples give, but reading through the documentation I think it should support a single value read.
Do you need to adjust your Instance and Attribute to read the appropriate parameter? Looks like you're trying to read parameter 1.01 the way it's set there.
EDIT: Looks like parameter 01.01 is indeed "Motor speed used". Does the value change at all if the VFD is running (if you are indeed able to start the VFD that is)?
EDIT: Looks like parameter 01.01 is indeed "Motor speed used". Does the value change at all if the VFD is running (if you are indeed able to start the VFD that is).
With the drive running, the data table reads as the attached picture. The other two EEM should be reading AMPS and FLOW, (starting at N17:60 and N17:120 respectively).
Maybe I need to scale the response data?
I don't know if I'm misunderstanding how to use the EEM instruction, but is the data table address inside the instruction supposed to be the same as the control block address of the instruction?
You put your finger on it: no, they're not !
Choose another data table or offset to hold the actual EEM message result, designated as the "Data Table Address (Receive Data)" in the EEM configuration window. You could stick it at N17:58 if you wanted to be really efficient on memory.
You're sending the data payload to N17:0 and N17:1, which are part of the EEM Control Block, so it's writing over the configuration every time the message completes.
I'll try testing this right now. The data in the receive table of the EEM instruction doesn't make sense either: it shows 52 and 59 in columns 0 and 1
edit: removed the other two EEM for now, using n17:60 as the receive data location, values still don't make sense, but I'm pretty sure it's scaling that's needed. Something to work on tomorrow.
Control words and data tables are organized and separate, communications works and data is coming in. I'm having issues with the EN and DN bits. I have a b3 XIC in front of each EEM instruction so I can work on one at a time, but the EN and DN bits stay true even if the bit is toggled high/low. The instruction also seems to keep running if the XIC is false when I enable the Continuous Run (CO bit) which I guess makes sense, but goes contrary to expected behaviour. Right now I need help figuring out how to reset the DN bit. The DN bit does not go true if the CO bit is true, as it just keeps repeating, but I'd like to eventually have these EEM instructions on a timer, to keep network data down.
I have the following Items connected for DH-485 per the drawing. SLC 5/03 HMI: Automation Direct EA9-T10CL+13Y19B054 1747-AIC #1: connected...
3,482
Hello, First I looked at Manuel and Plctalk but I did not find or maybe not understand. How I can connect ''HTL / Push pull-24 volt encoder'' to...
2,648
Hello I will make it short and sweet. I need the cable that goes from the slc 501 to the 1747-UIC RJ-45 connection. From what I can find it...
1,431
All, Thanks for any help. I am currently changing out an 1747-L543 processor over to an 1747-AENTR card so that I can now run this rack from an...
2,388
hello genious i have one slc cpu and with the slot of 1747-SN scanner module. and it is connected in to 2 slaves by 1747 ASB modules with...
2,193