We have an Emerson 3051SFA DP annubar flowmeter configured for square root output. We don't normally use annubars so although vaguely aware of what is involved I've never written or commissioned software myself. The issue was with the correction factor to normalise the flowmeter output at different pressures and temps.
Some old software I was given (which supposedly worked OK but we've all heard that before...) gave normalised flow Qn as:
Qn = Qa x (273/tm) x (Pm/1.013)
where tm was measured abs temperature and Pm measured abs pressure (units bar and °C)
This gave rubbish results but seemed to be mathematically wrong (i.e. it's based on P1.V1/T1 = P2.V2/T2 right?) and was missing the datasheet pressure and temp conditions at flow so I wasn't surprised. I tried:
Qn = Qa x (tm/td) x (Pd/Pm)
where td and Pd were abs temps/pressures from the data sheet.
Results at least seemed sensible but the gas composition wasn't fixed and we had no other flow meter to compare with so no one seemed to know for sure. An instrumentation guy then told us we should be using:
Qn = Qa x sqrt[ (tm/td) x (Pd/Pm) ]
I couldn't work out why we needed to root the correction factor and he seemed to struggle to explain it. But then it's not unusual for a guy with years of experience to forget the first principles when he's away from his desk and an internet connection plus it was outside my experience anyway, so we gave it a go.
Our customer was happy enough due to the varying gas composition and this device was only really for indication but I'd like to know what the proper/practical way to do it is. Any ideas?
An internet search (including on this site) and discussions with the supplier have left me none the wiser, various often complex equations have been bandied about but no clarity. What have others used?
Some old software I was given (which supposedly worked OK but we've all heard that before...) gave normalised flow Qn as:
Qn = Qa x (273/tm) x (Pm/1.013)
where tm was measured abs temperature and Pm measured abs pressure (units bar and °C)
This gave rubbish results but seemed to be mathematically wrong (i.e. it's based on P1.V1/T1 = P2.V2/T2 right?) and was missing the datasheet pressure and temp conditions at flow so I wasn't surprised. I tried:
Qn = Qa x (tm/td) x (Pd/Pm)
where td and Pd were abs temps/pressures from the data sheet.
Results at least seemed sensible but the gas composition wasn't fixed and we had no other flow meter to compare with so no one seemed to know for sure. An instrumentation guy then told us we should be using:
Qn = Qa x sqrt[ (tm/td) x (Pd/Pm) ]
I couldn't work out why we needed to root the correction factor and he seemed to struggle to explain it. But then it's not unusual for a guy with years of experience to forget the first principles when he's away from his desk and an internet connection plus it was outside my experience anyway, so we gave it a go.
Our customer was happy enough due to the varying gas composition and this device was only really for indication but I'd like to know what the proper/practical way to do it is. Any ideas?
An internet search (including on this site) and discussions with the supplier have left me none the wiser, various often complex equations have been bandied about but no clarity. What have others used?