Can I have a double word in SLC 5/05. Actually I want to send this double word value over devicenet.
 
You can have a DWORD resultant from a math instruction that overflows the 32767 maximum value for an Integer. When a math instruction overflows, the unsigned remainder is put into the regular destination address and the 32-bit result is placed into a special "Math Register" comprised of processor status words S:13 and S:14.

The data is only there until some other instruction uses the math register, so immediately after the math instruction that results in overflow, you should COPY these out into 16-bit holding registers to get ready to put them into the DeviceNet I/O or message area.

I've done this to set the Index position (400,000 counts or so) for an A-B Ultra3000i motion controller on DeviceNet and it works fine. In that case, I didn't have to reverse the order of the Words, but for your device you might, depending on what sequence it expects the data bytes on DeviceNet.
 
Of course, having a math overflow creates a minor overflow fault, that will result in a major fault at the end of the scan. If you plan to use this, program a OTU S:5/0 to clear the minor fualt before the end of the scan to prevent it from becoming a major fualt; causing the processor to shut down.

I think that you have to set S:2/14 to enable the double word functionality. I have never used this option. Im sure someone here will explain more thoroughly.
 
Last edited:

Similar Topics

Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
Replies
1
Views
534
Hi, I am currently reading a Modbus value from a Device, through TCP, going into our 400 series plc. The Modbus value is a real value, and it is...
Replies
27
Views
7,598
Hello How to convert dword to bit in Siemens plc s7؟ Thank you
Replies
15
Views
2,800
Hi, In Proficy Historian I have a tag connected with Double Integer / DWord configuration. In the PLC it is a Time format. Can that be a problem...
Replies
0
Views
1,206
Hello Everyone, I am working in Automation Builder software and PLC is PM554-ETH. I am doing communication over Modbus-TCP...
Replies
2
Views
3,279
Back
Top Bottom