For an upcoming project, the GC has chosen this wire:

https://www.mayerelectric.com/itemDetailFilterPH.action?codeId=1189529

There will be three nodes, 700 feet will be the longest run. I don't like that cable, not sure it will work. I thought it was at least an unshielded twisted pair, but it doesn't even appear to be twisted. I can ask him to change it, but I want to be sure before I cause an unneeded expense for him.

Any thoughts?

Thanks,
Paul
 
It's hard to prove a negative; I can't say for sure that an untwisted pair will not work, but I can say that a twisted, shielded pair is recommended and has a far higher probability of working reliably.


The EIA-485 standard does not, to my knowledge, actually recommend a wire type. It does recommend 120 ohm characteristic impedance.

I would bring him a couple of vendor's recommended product sheets for RS485:

Belden's RS-485 cables


General Cable's recommendations for RS485
 
Whether it works or not depends on a long list of environment variables you don't know and the unpredictable ways in which they will interact. I've heard of RS-232 serial runs of 100 ft run in the same conduit as power working almost flawlessly (whenever a motor started, the surge would sometimes corrupt the data during transmission). That doesn't mean it's a good idea, of course.

I guess the selling point could be, without running shielded cable you're risking mysterious, hard-to-troubleshoot errors cropping up. The added cost of a shielded cable is well worth it if it avoids risking the expensive nightmare troubleshooting a network issue can be.
 
I already fired off an email to tell him I didn't like it and can't be sure it will work. I found an article to support my case and recommended Belden 3106A.

Thanks for the feedback.

As it turned out, he has not used any of that "speaker cable" yet and thinks he can return it.

Here is one of the links I sent that may prove useful for future readers of this thread:
http://www.chipkin.com/rs485-cables-why-you-need-3-wires-for-2-two-wire-rs485/
 
Last edited:

Similar Topics

Having trouble wiring my device into the 1763-NC01 adapter and can't find any good documentation online. The adapter has connections labeled...
Replies
5
Views
10,975
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
221
Does anyone know of an AOI using the user ASCII protocol select on the L6x controllers that will talk Modbus RTU using RS-485? Thanks, Trevor...
Replies
1
Views
129
Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
Replies
0
Views
187
I am trying to figure out some communication specifics for a Modbus RTU network that I will be integrating with and could use some help to make...
Replies
9
Views
2,081
Back
Top Bottom