AOI for Modbus rs-485 on L62 serial port?

tlf30

Lifetime Supporting Member
Join Date
Apr 2021
Location
Deadhorse Alaska
Posts
196
Does anyone know of an AOI using the user ASCII protocol select on the L6x controllers that will talk Modbus RTU using RS-485?

Thanks,
Trevor

EDIT: Or a dirt cheap used prosoft MVI56-MCM module? This is for my bench at home. I'm building some wireless modbus level indicators for my heating oil tanks.
1712175165010.png
 
After some research, I found that the serial port only does RS-232. Which surprised me because I always thought DH-485 was done using RS-485. I guess I need a converter. I also found that Rockwell has a AOI for serial Modbus RTU, it was hidden deep in the knowledge base, my previous searches failed to find it.
 