Mp277 screen gonw white

jithesh

Member
Join Date
Mar 2016
Location
India
Posts
6
Two days back an MP277 touch panel in one our control posts went white blank. When the problem was first observed there were coloured vertical lines in the screen. On power resetting the screen went white. There is one common DP/MPI/PPI RS422/485 port with a DIP switch to which the profibus connector was connected. Then there two USB ports and a LAN port. We had transferred the program via LAN one year back. I would appreciate help in this matter.


Thanks in advance,
Jithesh
 
It sounds like your MP277 needs repair/replacement.

Is your PLC an S7-300/400 PLC? If so, you could temporarily get control of the machine by:

- disconnecting the MP277 from the Profibus network
- connecting a computer with WinCC flexible installed to the PLC with your PC Adapter or CP5711 adapter
- Start RT (runtime) from within WinCC flexible

Make sure in Set PG/PC interface that the Profibus address is the same as the MP277 before connecting.
 
It sounds like your MP277 needs repair/replacement.

Is your PLC an S7-300/400 PLC? If so, you could temporarily get control of the machine by:

- disconnecting the MP277 from the Profibus network
- connecting a computer with WinCC flexible installed to the PLC with your PC Adapter or CP5711 adapter
- Start RT (runtime) from within WinCC flexible

Make sure in Set PG/PC interface that the Profibus address is the same as the MP277 before connecting.


We are using an S7-400 PLC. Originally we were using a TP270 10" touch panel. Last year its screen went white all of a sudden. It was programmed with PROTOOL.
So when we replaced it with MP277 touch panel the program in protool was converted in WinCC flexible in another computer.
Our PLC pg unit has only protool installed in it and it is not possible to install winCC in the PG unit since its OS is Windows XP sp2. WinCC flexible will run only in OS from XP sp3 onwards.
 

Similar Topics

I currently have 4 siemens mp277 10 inch touch screens I deal with. Lately 2 of them have been giving erratic touch screen results. To specify...
Replies
7
Views
1,785
Hello, I am facing some issue on my siemens control panel on which the screen is all black. This control panel (mp 277 10" - 1P6AV6...
Replies
5
Views
3,309
Hello All, I'm looking for a little help. I'm an onsite controls engineer, we have had 2 new bits of kit installed, one with a comfort screen...
Replies
1
Views
2,769
Hi I have a siemens MP277 screen. After I made some changes ( add a few alarm messages) and download some buttons on screen disappear (those...
Replies
8
Views
2,729
Good day, May I ask, what do I need to perform MIGRATION of HMI program from Siemens MP277 10" Touch hmi to TP1200. I already have WinCC Flexible...
Replies
0
Views
160
Back
Top Bottom