Had a quick search on here but haven't (yet) found my answer...

Is there a way in L5k/S5k to disable a user from forcing outputs...completely?

Reason: I have a machine that if two outputs are forced on simultaneously, then two pneumatic cylinders are going to crash into each other and bend stuff... not a danger to the operator as it's inside a chamber with safety guarding...

but if I had bubba willy nilly forcing stuff to try and solve a problem it might not end well..

In the logic I have interlocks (software) to prevent this from happening in auto mode, and I will be providing in the HMI a maintenance screen where they can toggle each cylinder (with logic that only one can be done at a time)

I can't do it via relay interlocks, because the signal is sent over E/IP to the pneumatic manifold header.

TIA.
 
What about fitting some pneumatic "NOT" valves to the cylinder pneumatic lines? This would work but obviously requires modifications to the machine.
 
I had thought briefly about doing that. I would prefer it done in software (processor lock) for the following reasons; there are 5x 5/2 valves in each machine that would need the pneumatic logic applied. There are 15 machines that run 24/7:365. I don't want unnecessary hard to debug (no feedback) stoppages caused by the NOT valves potentially failing.
 
I'm not sure if AB have a feature like this, but in Schneider Unity processors there is a function block for forcing and unforcing an I/O on or off through logic. I normally use it only for simulation of code. But If an AB equivalent exists you could just "un-force" the particular point each scan. Will confuse and infuriate bubba, but at least there won't be mangled metal.
 
I can't apply a software change to the tech's laptop's as I'm a contractor so that's outside of my remit.

I can't remove the key in run mode as maybe I want to go online with the controller from home (1.5 hours drive from site).

If it turns out this is not possible, is there a GSV instruction that tracks force activity? At least that way I could provide an audit log in the SCADA.

Thanks
 
Yes, you can use a GSV to detect forces as installed and or enabled. Use the GSV with the Module Object. Skip the instance as it doesn't apply and you can select ForceStatus.

OG
 

Similar Topics

I recently did a program conversion from logix 500 to studio 5000 and when machine runs it depends on two ton instructions to keep the machine in...
Replies
17
Views
567
Does anyone know how to set the background colors of instuction blocks (TON, MOV, etc)?
Replies
1
Views
162
Hey Guys, I am looking for a cr@cked version of Studio 5000 Logix Emulator V28 or Rslogix5000 V21, which will work with my current emulator...
Replies
1
Views
318
Good Evening , I have version 28 of Studio 5000 from a few years ago . If I got a new CompactLogix CPU , what is the lowest version of...
Replies
4
Views
497
Back
Top Bottom