Tags connection between panelview standar and compact logix

If you have a PanelView Standard terminal, it's easy to get confused by modern advice about PanelView Plus or PanelView Component terminals.

On this Forum, we suggest strongly that novice PanelView users provide the full part number of their terminal, so that we can tell exactly what functions and features it supports.

The PanelView Standard terminals generally do support ControlLogix and CompactLogix, both by using SLC/PLC data mapping and by using native ControlLogix tag addressing. The Ethernet models can even provide an I/O Adapter object for very fast pushbutton performance.

Because the PanelView Standard preceded the ControlLogix, support for all the ControlLogix tag data types was introduced gradually. The firmware revision of the PV Standard terminal may be important.

If you have TechConnect, a very good program example is in RA Knowledgebase Article 20512.

Otherwise, I'd say start with the Quick Start guide for PanelBuilder 32:

http://literature.rockwellautomation.com/idc/groups/literature/documents/qs/2711-qs003_-en-p.pdf
 

Similar Topics

How to read/write tags using class3 connection with omron Nx/Nj Plc? when i am seeing wireshark packets for my existing connection its shows as...
Replies
0
Views
712
in FTV ME Version 9.0 i want to have 2 tags for the global connection "Replace Display Number" - is this possible? i have 2 plc short cuts...
Replies
2
Views
1,336
Hello, I am working with Factory Talk View 8.2 SE (Local). I am having an issue with the client viewer “holding connection” with the tags. I open...
Replies
1
Views
1,932
I look after the data collection for our plant. At this point I have 75 Rslogix 5000 series PLC's communicating via a uni-cast network to a...
Replies
3
Views
3,266
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
Replies
2
Views
63
Back
Top Bottom