Hi,

I am new to the PLC's. Can someone enlighten me regarding the Alarm relay on the Schneider BMXCPS3020 power supply and does the digital input module need to be powered with 24VDC to make it working?

How to configure the M340PLC and installation of Unitypro.

Does the unitypro has an emulator like in Micrologix to check the ladder logic.


Please help me. Thanks

Regards
Immanuel
 
Alarm relay closes when the PSU is powered up and the processor is in run mode.

DDI module requires 24V plus 0V for the IO fault light to clear. Module still works without this but shows a fault.

Install unity - autorun from CD. Super easy. Run licence application after, register or software runs for 20 days in demo mode.

Connect to the PLC using USB port the first time. Super easy.

There is a simulator yes. Once you install unity it is a stand alone application you'll find in the unity folder.
 
Hi Saffa,
Could you please help me with this?
I am using BMXP341000 processor and a NOC04001 Communication module. I have seen some you tube videos where people configuring the ethernet are choosing (CPU) instead of default NOE (I am new to this and have no idea). I am doing my final year engineering project and trying to build a test bench using Schneider M340 PLC. Can you help me to fix the issue looking at the error message.

" This CPU(BMX P34 1000) or its version 9V 02.700 dosent support the security services. Enable all fields9ftp/http0 or replace the current CPU"

I am confused with the family we choose (NOE or CPU). If I choose the CPU thats the error message that pops up. Anyway I am unable to link the ethernet to the comms module. Your advice is much appreciated.

Regards
immanuel
 

Similar Topics

Hello all, I am wanting to update the system clock via NTP in the M580/M340. I'm aware that we are able to connect to a NTP in the controller...
Replies
4
Views
129
so i have an isssue where if the serial port of an M340 plc disconnect from the screen it would retain the values of the variables being sent...
Replies
1
Views
913
Hello, I'm having a hard time understanding how to get a Modicon M340 to pull a Modbus address from an ABB Totalflow via Ethernet. I set up a port...
Replies
5
Views
1,151
Hello, this is a message for specialists in Schneider, I am trying to establish communication in modbus tcp between a schneider M340 (P3420302)...
Replies
2
Views
1,606
I need to establish communication between Schneider M340 and S7-1500 PLC. I am using gateway converter for MODBUS TCP TO PROFINET protocol...
Replies
12
Views
2,979
Back
Top Bottom