Allen Bradley Kinetix5500 STO control by Omron safety controller

cocoroco89

Member
Join Date
Mar 2016
Location
Kitchener
Posts
13
Hello,

I have an inquiry about controlling Servo drive STO(Safety Torque Off) by following components.

-. SERVO DRIVE: 2198-H040-ERS2
-. PLC Controller: 1769-L33ERM
-. Safety Controller: G9SP-N20S

Would it be possible to control STO with the components above?
 
As far as I know, it won't work. The alternatives would be:

1) Hard-wired STO.
2198-H040-ERS
1769-L33ERM
G9SP-N20S

2) GuardLogix
2198-H040-ERS2
1769-L3xERMS
 
Hard-wired STO can generally be switched by any safety controller or safety relay.

It is just a set of monitored safety inputs on the drive.

I don't see why it wouldn't work.

P.S. Jeev... Viscount?
 
Thanks to all.
I got the answer from RA that the component list I mentioned wouldn`t work. ERS2 servo drives require integrated safety controller that can issue STO command over Ethernet. It is shame that ERS2 blanked STO terminal block. It would have been so much more flexible to either cases of hardwired STO or STO over Ethernet.
 

Similar Topics

Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
Replies
15
Views
252
Hello, Does anyone have one of these cables and willing to open the case so I can see the cable connections inside? 2707-NC5 I have sourced the...
Replies
3
Views
84
Currently trying to find: micrologix ethernet interface 1761-NET-ENI AIC to micrologix 761-CBL-AM00 Ser C cable These are used for micrologix...
Replies
3
Views
133
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
173
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
459
Back
Top Bottom