Allen Bradley Kinetix5500 STO control by Omron safety controller
cocoroco89
Mar 2016
Kitchener
Hello,
I have an inquiry about controlling Servo drive STO(Safety Torque Off) by following components.
-. SERVO DRIVE: 2198-H040-ERS2
-. PLC Controller: 1769-L33ERM
-. Safety Controller: G9SP-N20S
Would it be possible to control STO with the components above?
As far as I know, it won't work. The alternatives would be:
1) Hard-wired STO.
2198-H040-ERS
1769-L33ERM
G9SP-N20S
2) GuardLogix
2198-H040-ERS2
1769-L3xERMS
Hard-wired STO can generally be switched by any safety controller or safety relay.
It is just a set of monitored safety inputs on the drive.
I don't see why it wouldn't work.
P.S. Jeev... Viscount?
Thanks to all.
I got the answer from RA that the component list I mentioned wouldn`t work. ERS2 servo drives require integrated safety controller that can issue STO command over Ethernet. It is shame that ERS2 blanked STO terminal block. It would have been so much more flexible to either cases of hardwired STO or STO over Ethernet.
Any one give solution for this fault. We are using AB Gaurd logix controller(5573s), resent days we are facing major fault in controller...
85
Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
356
Hello, Does anyone have one of these cables and willing to open the case so I can see the cable connections inside? 2707-NC5 I have sourced the...
105
Currently trying to find: micrologix ethernet interface 1761-NET-ENI AIC to micrologix 761-CBL-AM00 Ser C cable These are used for micrologix...
141
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
188