Hi guys
i have some PF4 VFDs out of service at the same time, maybe it is the problem of incoming 480 VAC, there is a MOL before VFD, I know MOL will trip if the load side current/temperture is too high, my question here is if the infeed 480VAC is not clean enough, will the MOL trip if there is high curren or voltage from the 480 source?
Thanks
1) If MOL = Motor Over Load, putting one AHEAD of a VFD is completely pointless. The VFD already IS the OL relay for the motor.
2) If what you are looking at is a Motor Protective Switch (see image), that's a different animal. That is the equivalent of a circuit breaker and many small VFDs are UL listed to have those ahead of them as the Branch Over Current Protective Device.
3) If you have multiple units (again, on the LINE side of the VFDs) that all turned off at the same time, all of your VFDs would have had to fail simultaneously. Since they are on the line side, and the VFDs would trip rather than allow the load to pull too much current, the only possible explanation would be that there was a severe voltage event that fried the diode bridges on all of those drives at the same time, meaning they are all toast and not repairable.
4) The only other possibility, IF those are the switches I showed above, is that they all have something like a Shunt Trip or Under Voltage Trip coil in them and something PURPOSELY opened them all at the same time. You would know because there would be 2 extra wires associated with each one,; if it's a shunt trip, they would be going somewhere else to a control circuit, if it's a UV trip, they would be tied to the line side wires.
To answer your question though, the harmonics on the input side COULD cause heating of the OL sensor elements, it's a known issue, but it's highly unlikely that multiple units would all trip at the same time, unless perhaps this is the first time it has been turned on and you have discovered a design flaw.