5000 V13, 1769sc-IF8U

DwSoFt

Lifetime Supporting Member
Join Date
Mar 2012
Location
Alberta
Posts
960
I wanted to tell a story about yesterdays experience for future help to others.

I arrived to a site to check and change a program for a Natural Gas Compressor. It has an L32E Processor.
Powered unit up, program was good. Go to go online, and it says i need to upload (backup isnt latest is why i normally have to do this) but would fault out.

A quick search here shows that RSlogix5000 v13 isnt meant for windows7, but many have made it work.
But i traced the error out to not having a module profile installed for the card (1769sc-IF8U, 8 universal analog inputs, i am using it for thermocouples, it can also do V,C,RTD)
I went to the manufacturers website(spectrum controls) Downloaded the AOP, installed it, still no luck. I thought of upgrading the firmware, but first called spectrum. they agreed, as the aop only starts at V15. I upgraded to v17, uploaded the program again and everything is good to go.

Anything else i could have done?

I have the link that helped me below, for reference to others:

http://www.plctalk.net/qanda/showthread.php?t=57234
 

Similar Topics

Hi, how do I convert 2x Integer registers to a Real? The two integers are from Modbus registers that contain a floating point value, I need to...
Replies
2
Views
103
What is the best way to extract the hour and minute from the register that comes from Yaskawa VFD. In studio 5000 I have a register saved as INT...
Replies
3
Views
102
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
Replies
0
Views
64
Hi all. I want to ask what may seem a stupid question, as I have a project to send live data to a Yeacode line printer which will print meterage...
Replies
10
Views
187
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
154
Back
Top Bottom