Sorry for disturbing you all in the first place. Hope you all don't mind to answer me a question... :)

Well, may I know is it bigger capacity drive Omron inverter cannot be functioning or control by plc when turning on a motor with smaller load? I got read a statement in that manual mentioning that, need to use a smaller size of capacity to drive the motor with 'about the same' load. I change to a smaller capacity of inverter and it works. Is it correct by the way or I missed out something? If is it correct, then any expert don't mind to provide some valuable explanation for me? Is it some other brand of inverter also giving the same problem like this?

Thank you to those who willing to spend time to read this thread... (",")


regards,
Freshy
 
Firstly, (/sigh) a PLC has nothing to do with an Inverter (VFD, AC DRIVE, SERVO DRIVE, VECTOR DRIVE, et al) other than telling it to "GO", "STOP", "REVERSE", "RUN AT x SPEED/TORQUE".

Now, second question, in general, an Inverter (VFD, AC DRIVE, SERVO DRIVE, VECTOR DRIVE, et al) should be close in size to the total rated load of the motor(s) it is connected to.

Yes, you can oversize a drive, but there are limits. You can probably run a 10KW motor on a 25 or 30KW drive, but trying to run a 10KW motor on a 100KW drive will (almost always) cause problems. The simplest reason? Drives need to control and monitor the current delivered to a motor. The feedback devices for current in drives are optimized to a certain range of loads, generally 30% to 150% of the rated drives capacity.

Running too small a motor can cause problems with stability in the current/torque loops, as well and potentially damage the connected motor.

Think of it like a load-cell. Controlling 50 to 100KG tension on a loadcell rated for 150KG isn't much of a problem. Controlling 10g to 20g on the same loadcell is.
 
On an open loop or V/Hz or scalar drive, mismatching isn't much of a problem within a 5 or 6 to 1 ratio.

The problem comes when trying to use Flux Vector or Sensorless Vector Drives. They probably should stay within about a 3 to 1 ratio to function properly. And, as stated above, the reason is poor detection and measurement of unexpectedly small motor lead currents.
 

Similar Topics

Hi All, What's the Difference between AB PowerFlex4 and AB PowerFlex40 inverters?:scratch:
Replies
2
Views
2,434
Hello, I have a problem with AO- and AA-Tags. When I use for example the tag AO_Test with the address 200 and type the value 1,2 in, the AA-Tag...
Replies
7
Views
1,413
As per the title. This might seem like a basic question to many, but I'm unclear about the difference between a coil ( ) and an application...
Replies
28
Views
4,042
Good Morning , I have 2 Frequency Drive panels to build and commission . It is for 2 pump systems . Just wondering , what is the...
Replies
4
Views
1,971
Hi Experts, Good day! What are the differences between PCS7 SIMATIC Batch and PM Control? Do you have any manual like "Getting Started "...
Replies
0
Views
813
Back
Top Bottom