hello,

this is to talk about siemens saftey integrated system, talk about what you know about it and how it works using dual channels and i think 2 seprate micros.
 
No, the dual channels and cpus is called an "H" (high availablity) system.
A safety integrated system is called an "F" system.
It is possible to combine F and H systems (in the S7-400 series).

I have heard how safety over ASi works, and I assume that safety over F CPUs and Profibus works principally the same.
Rather than having hardwired signals between the safety devices (E-Stops, light curtains, etc.) and safety relays, the CPU sends a coded message to the device, which in turn must respond with another coded message. If the CPU doesnt recieve a proper return message it turns off the output devices that the safety devices shall safeguard.
 
It does not use two micros, just one.
However, it solves its logic in both the bit logic section of the CPU as well as the word logic section, then compares the results, thus getting the equivelent of having two diverse CPUs solving the logic (two channel).
This contrasts to the Pilz method of getting the same result via the use of three different CPUs in their safety PLC (two channel, plus one just to be sure).
 
ok wait now, can some one explain to me the F and H systems, whats the diffrence and how do they work, thanks
 

Similar Topics

What he have is a HMI2GO unit ( KTP900F) and we use a safety relay to trigger our e-stops. What the tech wants to do is guard against e-Stop on...
Replies
2
Views
1,863
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
7
Views
130
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
141
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
300
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
112
Back
Top Bottom