sorry...you'll only be able to follow that link from the corporate home page.
here is the first section of Art130 cut & pasted from the NFPA site...
ARTICLE 130 Working On or Near Live Parts
130.1 Justification for Work.
Live parts to which an employee might be exposed shall be put into an electrically safe work condition before an employee works on or near them, unless the employer can demonstrate that deenergizing introduces additional or increased hazards or is infeasible due to equipment design or operational limitations. Energized parts that operate at less than 50 volts to ground shall not be not required to be deenergized if there will be no increased exposure to electrical burns or to explosion due to electric arcs.
FPN No. 1: Examples of increased or additional hazards include, but are not limited to, interruption of life support equipment, deactivation of emergency alarm systems, and shutdown of hazardous location ventilation equipment.
FPN No. 2: Examples of work that might be performed on or near exposed energized electrical conductors or circuit parts because of infeasibility due to equipment design or operational limitations include performing diagnostics and testing (e.g., start-up or troubleshooting) of electric circuits that can only be performed with the circuit energized and work on circuits that form an integral part of a continuous process that would otherwise need to be completely shut down in order to permit work on one circuit or piece of equipment.
FPN No. 3: For voltages of less than 50 volts, the decision to deenergize should include consideration of the capacity of the source and any overcurrent protection between the energy source and the worker.