i dont know Randy but i would say Ron hit it spot on...
From rs5000 on line help...
The MCR instruction, used in pairs, creates a program zone that can disable all rungs within the MCR instructions.
When the MCR zone is enabled, the rungs in the MCR zone are scanned for normal true or false conditions. When disabled, the controller still scans rungs within an MCR zone, but scan time is reduced because all the outputs in the zone are disabled.
When the MCR zone is disabled, the rung-condition-in is false for all the instructions inside of the MCR zone.
When you program an MCR zone, note that:
§ You must end the zone with an unconditional MCR instruction.
§ You cannot nest one MCR zone within another.
§ Do not jump into an MCR zone. If the zone is false, jumping into the zone activates the zone from the point to which you jumped to the end of the zone.
§ If an MCR zone continues to the end of the routine, you do not have to program an MCR instruction to end the zone.
Important: The MCR instruction is not a substitute for a hard-wired master control relay that provides emergency-stop capability. You should still install a hard-wired master control relay to provide emergency I/O power shutdown.
Do not overlap or nest MCR zones. Each MCR zone must be separate and complete. If they overlap or nest, unpredictable machine operation could occur with possible damage to equipment or injury to personnel.Place critical operations outside the MCR zone. If you start instructions such as timers in a MCR zone, instruction execution stops when the zone is disabled and the timer is cleared.
D