sorry I'm new in ti505 programming,i don't understand how i can choose the resolution for timer TMR (by number?)

Thanks
 
There are two timer types in 505-series PLCs - TMR and TMRF

The TMR has a maximum value of 32767 x 0.1s = 3276.7 secs
The TMRF has a maximum value of 32767 x 0.001s = 32.767 secs

These types are not dependent on the timer number you choose. You can program each one as either a TMR or a TMRF (but not both in the same program!)

Regards

Ken
 
Since you are new to the 505, I will remind you that counters and timers use the same memory area, so each timer and counter must have a unique number. For example if you have timers 1-10, then the first number available for a counter is 11. If 11 is used for a counter, and you need another timer, the next timer would be 12.

This may be something you were already aware of but it never hurts to be careful.
 
that's a good point, ken, threw me for a loop when i started on the 505. also in the documentation, looking at X34 i saw it was a light, which is an output. so if you have a Y34, you can't have a X34, like the 405. but it will give you that in the documentation.
 
Yes the inputs and outputs also use the same memory area, so you cannot have an input and output with the same number. But this can be useful when connecting an HMI. Rather then having two polls, one for the X's and one for the Y's, you can use a single poll that reads them all.
 

Similar Topics

Hi. I have 2 files where I would like to see the ladder logic differences (similar to the Rockwell compare function). I am using TISoft Siemens...
Replies
1
Views
1,265
Hello everyone, this is a noob speaking. I have no idea about plc's, just some basic things. So, I work at a factory in greece and we have a...
Replies
4
Views
1,149
I am trying to figure out the math with two U16 values that are converted to a Float(F32) in the TI so as to duplicate in a Siemens S7-1500. Seems...
Replies
13
Views
2,083
Stick a fork in it? Circa 1995 control system on a critical machine. Less than 100 Digital IO, less than 10 analog IO. I believe we can remove...
Replies
4
Views
1,648
Hi, I'm in an plant that uses TI505's. They have started upgrading to compactlogix but have reached the stage that they need PLC to PLC coms. TI...
Replies
3
Views
2,338
Back
Top Bottom