Allen Bradley Microlgix fault overide

strech

Member
Join Date
May 2005
Posts
7
Sending a Micrologx 1200 unit to a rural area. The customer has no way to go online and reset faults or veiw the program. Is it standard practice to set the S:1/12 to 1 and the S:1/8 to 1 in order to overide any faults at power-up? Does anything else need to be changed from the factory settings? Thanks
 
That is all I ever do with the remote micrologix units. I set the bits in the data table and make a big bold comment in the first rung of the main routine that this has been done and why in case someone else tries reseting status bits at a future date.
Regards Alan Case
 
Cheap insurance: an EEPROM module.

Be sure you carefully write and test any math logic that has the ability to overflow, including counters and MUL and DIV instructions. That's the single biggest cause I've found of rural or remote controllers that require expensive service visits.
 
Ok

By setting S:1/8 enables fault override at powerup.
By setting S:1/12 sets the processor to run always.

Ken / Alan

I assume this is doen so if the PLC power is cycled S:1/8 clears an error that may have existed and S:1/12 means the processor will continue to run despite a math overflow error and other problems?
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
357
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
Replies
0
Views
90
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
16
Views
584
Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
Replies
6
Views
425
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
145
Back
Top Bottom