I have a A/B 1771-OA card that has enough leakage to keep a 120v solenoid powered. Should I add a MOV or simply replace the card?
 
MOV won't help. Leakage for that card should be 2ma maximum. If its greater than that than I would suspect the card. Can you check it against the solenoid specs?
 
Low power loads may need some parallel resistance to reach the minimum load spec.

I haven't seen the problem with the 1771-OA but it was very common with the 1771-OM.
 
Put 16K+/1w or 12K+/2W resistor in parallel with load.
This will fix it.
It's imortant to have in parallel.
 