OP270 or OP27 instead of OP25/A

tulip

Member
Join Date
Oct 2005
Location
ist
Posts
236
hi people,
I have got s5-115u (cpu943b)that communicated OP25/A.
I want to change this OP25/A with new one.Therefore I could not decide whether OP27 must be use or OP270.IF I use OP270,Can I meet what kind of problem?Is the additional software for communication needed for this?For example standard FB's..
thanks for your efforts....
 
I dont know if it is necessary with standard FBs or not, but I suspect that OP27 and OP270 work the same as OP25 connected to an S5 via the PG port.

A small snag:
The OP27 has the same TTY port for the connection to the S5 PLC.
The OP270 only has a RS232 port. So it needs an aditional adapter to connect to an S5 PLC.

The OP25 program will convert easily to OP27.
When converting from OP25 to OP270 there will be a number of things that cannot be converted. This must be checked manually.

On the other hand, the OP27 is allready obsolete.
The OP270 is the current model (there is allready an OP277 under way though).
 
Thanks .I decided to use OP270 despite to difficulty.Now single thing for rest whether standard FB's is needed or not.?...
 

Similar Topics

I have converted an OP27 to OP270 but the problem is I am missing the interface area in the area pointers, what can I do to get it back?, I have...
Replies
1
Views
3,407
Hi guys, How do take backup siemens op270. Do you have any idea please help me. your support and help would be appreciated. Regards. uj
Replies
8
Views
2,643
I migrated OP270 backup program to OP277.Old HMI was using protool now new one is wincc flexible.Everything is okay.But OP270 HMI was using...
Replies
2
Views
2,071
Received the following Error Message during Transfering the HMI project files(16 files compeleted) to Simatic OP270-10" "The Connection was...
Replies
12
Views
3,405
Hi all, I need to modify some alarms in an OP270. Could somebody help me with correct procedure for uploading from this type of HMI. Can't find a...
Replies
4
Views
4,412
Back
Top Bottom