Its funny, when you mentioned air compressors the first thing I thought of was a situation where all were not needed on 3rd shift..example; a dairy processing plant at night does not run production, that is when maintenance and cleanup is performed.
I have actually developed a system for that purpose but used their in house computers etc so did not keep a copy of the program.
I looked at the DL06 manual and the date and time are kept in Vmem locations, look at Chapter 5 page 171-2
http://web2.automationdirect.com/static/manuals/d006userm/d06uservol1.pdf
The equivalent, I think, to the AB EQU instruction for AD is ANDE, look in Chapter 5 page 28.
Alternate may depend on the compressors, in some cases one compressor may be much larger than the others and is always the primary. If the compressors are all the same size and able to handle the lighter load then too alternate you initially start with one then use a "WAS" bit to show it was last used.
As an example lets say you have 3 compressors, called 1, 2, and 3. Monday compressor 1 was "lead" compressor so runs all day/night. Tuesday the plc looks at what compressor "WAS" left running, 1 in this case, and sets 2 to run all day. Each time it sets one it resets the others "WAS" bit..ie 2 resets 1's "WAS" and 3 resets 2's "WAS" bit.
Using that method allows you to actually do more with little effort. A pressure sensor could also be incorporated to initialize the compressors as needed i.e. you want to maintain a constant 90psi, if the system pressure drops then add the next compressor.