gimmephone Member G Join Date Mar 2005 Location Windsor, Ontario Posts 34 May 2, 2006 #1 I am almost certain I cannot but is it possible to use the I/O modules for the SLC 500 for the Micrologix 1100?
I am almost certain I cannot but is it possible to use the I/O modules for the SLC 500 for the Micrologix 1100?
rdrast Lifetime Supporting Member Join Date Apr 2003 Location South Carolina Lowcountry Posts 5,544 May 2, 2006 #2 Nope.
TConnolly Lifetime Supporting Member Join Date Apr 2005 Location Salt Lake City Posts 6,152 May 2, 2006 #3 Only if you put a SLC5/05 in the rack with the 1746 IO and have the ML1100 message data to the 5/05 to place in the IO image table. I have no idea why you would do that though.
Only if you put a SLC5/05 in the rack with the 1746 IO and have the ML1100 message data to the 5/05 to place in the IO image table. I have no idea why you would do that though.
Ken Roach Lifetime Supporting Member + Moderator Join Date Apr 2002 Location Seattle, WA Posts 17,497 May 3, 2006 #4 The expansion I/O for the MicroLogix 1100 is very straightforward; you can use any four 1762-series expansion I/O modules. These modules are used for both the MicroLogix 1100 and 1200. http://www.ab.com/programmablecontrol/plc/micrologix1200/io.html
The expansion I/O for the MicroLogix 1100 is very straightforward; you can use any four 1762-series expansion I/O modules. These modules are used for both the MicroLogix 1100 and 1200. http://www.ab.com/programmablecontrol/plc/micrologix1200/io.html