Hi guys,
Found the forum by Googling up answers, but I'm not seeing any good ones yet.
I have a DH485 network with 7 nodes on it. It has a variety of SLC's (01's/ 02's), one ML1000 and one ML1200. The SLC's are using the old AIC, while the ML's are using AIC+.
One SLC is a 5/04 being used as a 'data concentrator' gathering limited info from the others on the -485. The 5/04 then talks to RSView 32 implemented SCADA on the DH+ channel (through Linx Gateway).
I know... it's a typical mess that you run into with these old networks.
This config has worked well for over four years. Now, we're trying to add one more ML1200 to the mix. Nothing fancy... just a few messages back-and-forth from the ML to the SLC 5/04. They're not even implmented in the code as yet.
When I plug the ML into the AIC+... the network IMMEDIATLY starts getting Comm timeouts on various nodes. It doesn't do this whe the AIC+ (by itself) is connected.
All the diag lights on the AIC+ look good.
Someone at AB told me this might be ML1200 firmware issue (the fw is probably an old rev. from a re-used PLC). Might this be the case? They also suggested I change the station number (the added ML is the last one in the daisy and has a lower number than some of the others).
The net length appears OK... possibly 2500 ft. total. Cabling seems OK, terminations OK, grounding OK.
I'm stumped. Anyone seen this kind of thing before....?
John
Found the forum by Googling up answers, but I'm not seeing any good ones yet.
I have a DH485 network with 7 nodes on it. It has a variety of SLC's (01's/ 02's), one ML1000 and one ML1200. The SLC's are using the old AIC, while the ML's are using AIC+.
One SLC is a 5/04 being used as a 'data concentrator' gathering limited info from the others on the -485. The 5/04 then talks to RSView 32 implemented SCADA on the DH+ channel (through Linx Gateway).
I know... it's a typical mess that you run into with these old networks.
This config has worked well for over four years. Now, we're trying to add one more ML1200 to the mix. Nothing fancy... just a few messages back-and-forth from the ML to the SLC 5/04. They're not even implmented in the code as yet.
When I plug the ML into the AIC+... the network IMMEDIATLY starts getting Comm timeouts on various nodes. It doesn't do this whe the AIC+ (by itself) is connected.
All the diag lights on the AIC+ look good.
Someone at AB told me this might be ML1200 firmware issue (the fw is probably an old rev. from a re-used PLC). Might this be the case? They also suggested I change the station number (the added ML is the last one in the daisy and has a lower number than some of the others).
The net length appears OK... possibly 2500 ft. total. Cabling seems OK, terminations OK, grounding OK.
I'm stumped. Anyone seen this kind of thing before....?
John