Siemens 224XP comms

Johnny T

Member
Join Date
Jul 2003
Location
Fife, Scotland
Posts
642
Hi

I have a job that requires talking to a barcode scanner and a PC via RS232. I wondered if a S7-224XP has two usable RS232 ports on it. I have been told that it has but I can't find any information on the net to confirm this.

Has anyone any experience of this PLC? Or any information on it?

Many thanks

JT ;-)
 
The two Ports on the S7-224XP are RS485! And can both be configured to read/write ASCII (named "FreePort" mode)

To connect an RS232 device, you need a RS232-RS485 converter. Siemens advices to your their PC-PPI cable (6ES79013DB300XA)

good luck!
 
Freeport

Leonardo said:
The two Ports on the S7-224XP are RS485! And can both be configured to read/write ASCII (named "FreePort" mode)

To connect an RS232 device, you need a RS232-RS485 converter. Siemens advices to your their PC-PPI cable (6ES79013DB300XA)

good luck!

I have used freeport out of one of their MPI ports to move data to a PC for internal use.
Yes, you do need a PC-PPI cable.
Keep in mind that once the MPI port is configured via the PLC program for Freeport, it becomes dedicated port.
You definetely need a dual port PLC for your application.
 
Many thanks for the responses. I'm receiving the scanner etc next week so I'll have a look at them and then buy in the PLC to test.

I didn't realise the ports were RS485 so that info alone has really helped me out.

Thanks Leonardo and bkottaras

Cheers

JT :)
 

Similar Topics

Dear Experts I have Siemens S7 200 CPU 224XP CN project file. can anybody tell me the details how can i unprotect all blocks. see attached file...
Replies
0
Views
3,488
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
159
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
141
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
300
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
112
Back
Top Bottom