Which versions of the 1771-ASB module are compatible with the 1756-DHRIO? Will versions A and B work?

Publication 1756-UM514B-EN-P - February 2003 indicates that A and B will work if a 150 ohm resistor is used.​
Table 8.3
Determining Resistor Rating and the Number of Devices Connected on Your Network
If your remote I/O network: Use thisresistor rating:
•​
1771-ASB/A 150 ohm

•​
1771-ASB/B 150 ohm
We are using RSlogix 5000 version 15.

 
I think the reason you haven't got any responses is that you asked a very specific question that you seemed to already have the answer for. The table you mention specifically calls out the series A and B modules. I would interpret this to mean they will work within the limitations mentioned. (i.e. 57K or 155K, 16 devices max)

I think you would get more responses if you would provide some context. What are you trying to do? I can guess that you might be upgrading an old PLC-2 to a ControlLogix, but that's just a guess. The older ASB modules may have additional limitations. I seem to remember that they could only do 2-slot addressing.

More info = more potential help.
 
Any series of 1771-ASB will work with a 1756-DHRIO scanner.

The 1771-ASB Series C added 230.4 kb/s data rate and "extended node" mode in 1991. You won't have those features, 1/2 slot addressing, or 32-point module support in Series A and B adapters.

But otherwise they are electrically and protocol-wise compatible with the 1756-DHRIO.
 

Similar Topics

L81 series processor, DHRIOE 1756 card, communicating to some old PLC 5 IO. Site wide power outage after power up everything is okay except 1...
Replies
6
Views
1,519
Hey everyone, Trying to bench test the I/O on a program that I converted from a PLC-5 processor to a ControlLogix processor but still using the...
Replies
21
Views
6,511
Hey everyone, Long time user of the site but this is my first time posting. I have a 1756-A4 rack with a Logix5562 in slot 0, 1756 ENBT/A in...
Replies
2
Views
1,957
I have a new project that is replacing the PLC-5/30 CPU with a 1771-ASB and ControlLogix CPU. This line is all blue-hose comms to 5 racks and the...
Replies
22
Views
4,820
Hi,I'm trying to migrate only CPU from PLC-5 to CLX and I/O modules are still PLC-5 series. I think, the migration works is almost done but I...