I am not certain what you are referring to regarding pages, however, here is an attempt to provide you with some information regarding your request.
You have the response time of your outputs, when initiated through the program. For a relay, it is typically 8 - 10 ms for the relay arm to go from a closed to open state or an open to closed state. Solid state outputs are typically faster than a relay.
A second possibility to what you are asking about is related to the scan time of a PLC, which includes the update of internal information. I can't speak for other manufacturers products, but with our hardware, the scan of a program goes first from left to right of the program rung, and then top to bottom of the program. (similar to reading english - left to right, top to bottom)
Some tend to word differently, when the update occurs. Basically, when the scan reaches the end of the program, it updates all internal information, registers, status of I/O, both external and internal. Once complete, it loops / returns to the top / beginning of the program and does the same thing all over again.
The above does not include immediate update I/O or high speed inputs tied to interupts.