Hi,

I have a problem with a flow measurement.

Could it be that I have a meachanical problem, see the attachment please.

There is a pipe of 50mm connected to a 50mm flow meter and the output is connected to an 80mm's pipe.

Can this be a problem ?

Isn't it so that the preasure decreases at the output when the pipe is larger then the input, that can speed-up the liquidflow ?

Anyone has an idea if that could be the problem, thanks.
 
You don't say what your problem is but since this is a mag meter you a) better have conductive enough fluid b) no air entrainment c) enough backpressure downstream to keep the flow tube packed when flowing.
 
the problem

The Problem is that it gives to less pulses to a countermodule.

So the measurement isn't ok. All parameters are okay
 
Questions...

Are you wired for Active or Passive mode pulse outputs?
What is your scaling for the pulse output?
What mode is the pulse width configured for?
Chances are if you're not exceeding your counter module input max frequency and you have the right pulse amplitude then this will be a pulse width issue. What model PLC and counter module are you sending the pulses into?
 
The nost common problem with flow meters is improper pipe configuration upstream and downstream of the meter. To give accurate readings the fluid must have a well developed uniform velocity profile. This is best accomplished by having sufficient straight constant diameter pipe upstream and downstream of the meter. Your supplier can give you their reccommendations, but usually 10 diameters upstream and 5 diameters downstream are the minimum. Otherwise you develop eddies and swirls in the flow that distort the measurement.

The expansion in pipe diameter right after your meter is a problem. You don't indicate how much pipe you have between the pump and the meter, but if it is a short distance that is another problem.

Some companies, like Vortab http://www.fluidcomponents.com/ or Canadian Pipeline Accessories http://www.cpacl.com/ make "flow straighteners" that can help compensate for poor installation conditions. Contact them for info, as well as your meter supplier.
 
asdffd
261i2w7.jpg
 
Hi Combo,
Tom is right. You should have a straight D50 mm of about 400 mm to 500 mm before the flowmeter, and the same after the flowmeter, and only than you can increase the D to 80mm if it is necessary.
 
To clarify & stop others form going off in different directions;
Does the Flowmeter display (if it has one) indicate proper flow indications i.e. rate & totalization? If there is no display, does a HART communicator or laptop indicate proper flow measurement? If you are measuring flow accurately then you do have, as I stated earlier, a pulse signal to input module issue. Granted, all the other posts are valid for flow conditioning considerations but let's clarify your situation.
 

Similar Topics

Hi folks, I am trying to fetch data from flowmeters of Krohne make using mlx1400 over RS485. The architecture as follows: Krohne device -----...
Replies
8
Views
1,387
Hi friends, I have a krohne flow meter optiflex5300. During liquid flow when it shows the actual flow value 2000 ml, physically its 2200 ml. I...
Replies
2
Views
1,859
Hi when i add the IFC 300 GSD File to Siemens CPU 300/ 400 Hardware Cataloug it appear in profibus PA Subgroup instead of Profibus DP.Is there...
Replies
0
Views
1,846
Dear all, I'm a using a flow meter for first time in my life, attached is the name plate details of krohne make flow meter. In this 4-20mA is...
Replies
2
Views
1,712
Hi, We have a krohne flow meter which controls the modulating control valve on our Blending machine which is electronically fault.We are in a...
Replies
2
Views
1,599
Back
Top Bottom