Hello James;
Yeah, looks pretty criptic, but tags follow the P&IDs in our plant:
_00_CH_01_YA_01 breaks down to:
Zone : 00 for chileers, 11 chiller evaporator, 41 for chiller condensor...
CH ; chiller, P : pumps, ZSO : valve open limit switch...
01 : number of the equiment (in this palnt we have 10 chillers)
YA_01 is the number of the alarm signal we expect from the chiller
This, by the way, is what we put on the wire labels.
Now for AL2_LCP_001_01:1:I.Data.0
This is the name we give to the CNBR module that connects the IO to the main processor.
AL2 is the symbol for our plant (AL-Ain-02)
LCP_001_01 signifies Local control panel 1, rack 1
:1 is the Controllogix indication for slot 1
:I.Data.0 means a digital input, channel 0
The easiest way for you tyo get familiar with this is to create your own IO configuration in RSLogix5000 and look at the Controller tags to see what tags are automatically created by the software (based on the modules you select in the cofiguration). Then create bogus tags that you will alias to the IO tags.
Here's a look at my configuration for the AL:2 project:
We've been using Controllogix in our projects for the past 4 years (since I've been involved anyway). Great platform.
Hope this helps,
Daniel Chartier