I need to make communication between a equipment that uses profibus and S5.

How can i do it? banghead

Anyboody could help me??

thank you all
 
First, what are you trying to talk to from the PLC? If you are just trying to get a few data points (<100) and going to an HMI, I would recommend using the programming port and using an AS511 driver. No extra cards or programming on the PLC end is needed. It is limited in speed to 19,200kb. If you want "full Blown" graphics, you can use profibus or ethernet. Both require using a card in the rack and some programming.
 
Hi

Siemens provide a CP541 communications module that provides a profibus link. You may still be able to download a manual form Siemens.de site. 6ES5-998-1DL11

If you are using 115 135 or 155 then you need the CP 5431
 
Hello!
You need the cards and also the COM profibus program !
Don't even think about doing it with the serial interface that is for point to point communications and causes a lot of work to get it functioning. Usually you can't even get field devices that support that protocol.
 
If you have solved the problem why not share the solution with us?
I'm trying to connect a 100U with the Cp541 and could do with a hint, cheers,
alexander
 

Similar Topics

I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
Replies
5
Views
592
I'm trying to figure out how to read the actual speed reference value from the move blocks, writing to a DB that is being sent to the VFD. For...
Replies
5
Views
2,656
Hi, i need to communicate with a profibus device input 24 byte output 6 byte i want to use my PID adress and not a INT so i can use crossref to...
Replies
2
Views
2,053
I am currently working on a project where the DP slaves of a CPU 412-DP have their I/O addresses allocated as 1/2 bytes. For example: The first...
Replies
1
Views
2,436
Hello all, I am hopeing someone on here can help me. We currently have our plcs connected to an ethernet network, connected to this is a desktop...
Replies
6
Views
4,304
Back
Top Bottom