Monitoring Controlnet RIO

DBLD99

Member
Join Date
Oct 2003
Location
USA
Posts
230
How have you guys monitored Controlnet RIO, We have probally 6 Racks of 1756 RIO and 2 1794 RIO over controlnet. I would like to monitor it in case of communication failure to take the correct action. I thought about monitoring the rolling timestamp on the racks with analog, but not all racks have analog.

Thanks for anyones time
 
You can use a GSV to get specific information on the adaper and modules. Just use the MODULE class, pick the module you are interested in and go from there. You will need to dig through the online help for the GSV instuction to see what the return code means.


Keith
 
Thanks, I should have waited to post for 5 more minutes because I finally found what I needed. Thanks for the help
 

Similar Topics

Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
Replies
1
Views
65
Our punch press has a SLC500 with HELM weight module (HM-604-WM) for tonnage monitoring. The operator enters the weight range on the HMI, which is...
Replies
9
Views
202
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
Replies
0
Views
118
Good day, we have 15 analog inputs, we need to log the data in excel and monitor these values through web browser. We're planning to go with Delta...
Replies
1
Views
123
I have several plc’s that I’d like to monitor Into our SCADA when the comms break or plc faults. These are (SLC-505 & Compact Logic PLC’s) I...
Replies
6
Views
745
Back
Top Bottom