i have created a project & assigned a shortcut in my RSLinx Enterprise communications setup for Local & Target, say SLC500, now if i m not wrong i have to use the same name (SLC500) while assigning tag value in my display screen, eg {::[SLC500]B3:0/1} inside the square brackets,

now my Q is if i change my shortcut (local & target) to different name say (ProjectX) then how can i change all the tag values in my graphical screens/display in a just 1 step, is there any way to do it, or i have to double click on each individual pushbuttons or indicators & change the name inside the square brackets to
{::[ProjectX]B3:0/1}

i m not connected online with PLC/ HMI right now, working offline.

thanks
 
Open the graphic display and select all of the objects (Edit menu - Select All). Then from the Edit menu select Tag Substitution.

Then the easiest thing to do is to just type in the name you want replaced (in the search field) and then type the name you want to replace it with (in the replace field). Deselect the "Confirm Replacement" and hit Replace.

Anywhere that name is used, even in an expression it will be replaced. However if you have created HMI tags this will not update the tags. This only fixes the "direct reference".

OG
 
The only problem is you have to do this replacement display by display. I wish there were a control that would let you select all tags in all displays and do the replacement for all of them at once.
 
bernie_carlton said:
The only problem is you have to do this replacement display by display. I wish there were a control that would let you select all tags in all displays and do the replacement for all of them at once.

The only other problem, is that this doesn't work when using tags defined in the HMI's tag database. Those you still have to go through manually.

As an aside, although the 'Direct Reference' tags are useful sometimes, I've stopped using them unless absolutely necessary. I've found it much more productive (and less error-prone) to build up a tag database manually then use direct references.
 
I tend to do the opposite. I rarely ever use HMI tags, opting instead for direct reference.

But, if I had done this with HMI tags, to correct this I would have exported the tags to a .csv and changed the tag info in Excel and then use search and replace.

OG
 

Similar Topics

Hello to all the knowledgeable people inside the computer screen, my problem at the moment is like the title says, l can't open projects in...
Replies
1
Views
1,325
Hi Working with some project guys who have replaced a controllogix processor previously using RSLogix 5000 V11 for a controllogix 5588E using...
Replies
10
Views
4,004
We have an older laptop here at work that has RSView Studio on it that isn't used for anything. They only use Red Lion HMI's now. I was thinking...
Replies
2
Views
1,514
I have an RSView SE 3.0 distributed application running on a Client/Server. Can I use FTView 7.0 to develop some new screens and or modify...
Replies
1
Views
3,905
Hello I am trying to get certain screen components to be visible unless an h/o/a switch is turned to manual I:0/8 being the input for the...
Replies
1
Views
1,343
Back
Top Bottom