PV and ControlLogix error 634

lllerena

Member
Join Date
Jun 2002
Location
Lima - Peru
Posts
21
Have you ever program a PanelView (in my case model 1000-ControlNet) and got a 634 error? this is because one tag is not found in the controloller,

But.....


Wich one ???

is there any tool to help with that? If I look in the PanelView screen by screen, I can find a group of tags that doesn't work, but it do not specifically indicates wich tag is the mistaken..... worst if the tag is an alarm.....

any help ? any experience?


P.D.
Iam using Contrologix 5555-Control Net-PanelView 1000
 
I have get it from Knowledgebase AB, hope this help.

ControlNet Error 634 PanelView Offline


Cause #1: The ControlNet cable from the PanelView is broken or disconnected.

Corrective Action: Fix and / or reconnect the ControlNet cable.


Cause #2: The PanelViews Node Number is greater than the UMAX (Maximum Unscheduled Node).

Corrective Action: Reconfigure the ControlNet network, or lower the PanelViews node address.
 

Similar Topics

Hello All, I have ControlLogix L81E with with PA50 Power supply, when I power-up the PLC, I have this fault : Major Fault T01:C061 non...
Replies
4
Views
3,103
I've recently replaced an 1756-L72 and 1756-ENBT with a 1756-L81E & 1756-ENBT2R on a ControLogix chasis. The machine ran fine for two days after...
Replies
5
Views
1,673
I have a 1756-L62 that is sending a message to give a 1769-L24ER a permissive bit to run. This system has been working fine for about 2 years...
Replies
4
Views
3,780
We are doing a conversion from a PLC 5 to controllogix. There are 4 remote racks in the system. Everything was working perfect until we upgrade...
Replies
2
Views
1,770
Hello :) I've already come up with a solution to the problem described below, so this is mainly a curiosity had the situation been different...
Replies
6
Views
3,715
Back
Top Bottom