We are doing a conversion from a PLC 5 to controllogix. There are 4 remote racks in the system. Everything was working perfect until we upgrade to a controllogix. Now we are getting an ade error on the remote racks that are 16 slots long. Already added a resistor to each rack and still same problem. On one rack we can only see 8 of the 16 RIO slots but not the last half.
 
This sounds like you have it configured for 1/2 slot addressing versus full slot addressing in your configuration. The error revolves around this issue.

Maybe someone changed the dip switch setttings on that remote rack by accident?
 
A single 1747-ASB can do up to 30 I/O modules and can support 32 Groups or 4 Racks. A rack is 8 groups.


A RSLogix5000 will only permit up to a full rack or 8 (I/O groups) on one ABS.


Add another ABS module under your 1756-RIO in your I/O tree and make it a full rack that will give 16 I/O groups.


You will have to configure multiple ABS modules in your I/O tree under the RIO to match your 1747-ABS settings.


You should check and see how the dip switches of the ASB is configured for I/O image then you have to set up your 1756-RIO and your ABS modules in your tree.


The modules in your CLX have to match the dip switch configuration in your ABS.
 
Last edited:

Similar Topics

We have a problem that has eluded us for two months now. There is a RIO rack connected to a SLC 5/05 (upgraded from a 5/04 five years ago). It...
Replies
9
Views
9,321
I have been asked to add new hardware to an old system. The PLC is a 5/04 SLC. In local rack, slot 25, is a 1747-SN connected to a 1747-ASB in a...
Replies
4
Views
2,501
hello genious i have one slc cpu and with the slot of 1747-SN scanner module. and it is connected in to 2 slaves by 1747 ASB modules with...
Replies
3
Views
1,982
I have 2 X 17 slot chassis connected with EN2T cards In Chassis 1 there is a 1756-L71 in slot 0 and a DHRIO in slot 1 + other cards The program...
Replies
5
Views
1,500
We had a storm last night, and the smoke got let out of some of our PLC equipment. I'm troubleshooting a link between a 1747-SN and a 1747-ASB...
Replies
6
Views
4,251
Back
Top Bottom