OK, first thing, PID is the control block - P&ID commonly means process & instrumentation diagram and if you say that it throws people's minds in that direction.
On point; if your setpoint will be in the range of 0.0 to 10.0, for example, store it in a float register F8:1 for this discussion. In the SLC, MUL F8:1 by 10 and store it in N7:1. This eliminates the decimal point but preserves the value. Then, using the SCP instruction, do SCP N7:1 with the range of 0 to 100 to the setpoint register in your control block woth the range of 0 to 16385 (16385 is the maximum setpoint value in the PID instruction.) So when your setpoint is at 8.5 (to use your value) the PID setpoint will be at approximately 13927. I hope this is what you were looking for.