Hello pa_1784;

Is it possible you mean a "backplane":

Extract from Siemens' S7-300 module data manual:
Backplane bus
The backplane bus is a serial data bus. It supplies power to the modules and is also used by the modules to communicate with each other. Bus connectors interconnect the modules.
Illustration of bus connectors:

Bus_connector.jpg


Hope this helps,
Daniel Chartier
 
Thanks

Hello Daniel,

Thanks for the reply regarding back plane.

regards,
Prashant Kulkarni.

Thermax Limited.

India.
 
Active Bus connector

I like to know if any of the intermediate modules in a back plane bus get spoiled will the modules after it, counting from CPU will still work or not?


I also heard of a term called active bus connector which allows the hot swappable modules in Siemens PLc's.

I like to know whether my theories were correct on this.
 
muthu_buddy said:
I like to know if any of the intermediate modules in a back plane bus get spoiled will the modules after it, counting from CPU will still work or not?

The modules after the defective one will carry on working. As far as I am aware hot swapping of modules on a S7 300 rack is not allowed, the PLC will go into stop when a module is removed, plus you are breaking the back plane bus link, so you lose the other modules after the removed one as well.

Paul
 
Hello Paul and Muthu_buddy;

I also heard of a term called active bus connector which allows the hot swappable modules in Siemens PLc's
hot swapping of modules on a S7 300 rack is not allowed

There is an active bus module that you can use on a remote S7-300 rack, not one with a CPU. It is used for example for a Y-Link setup (2 x IM157 as redundant DP-slaves on a S7-400-H system). But as you stated, Paul, on Rack 0 (which contains the CPU) this is not possible.

Hope this helps,
Daniel Chartier
 

Similar Topics

Dear All, Currently i'm working with Endress Hauser flowmeter and AB PLC and try to integrate with 2 items. Flow meter spec using is Promass...
Replies
3
Views
71
merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
Replies
1
Views
255
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
735
Hi Any one here please helpmein simulation of s7 300 plc program with factory io. how to connect. plcsim 5 doesnot have option of s7 300 ..:
Replies
2
Views
1,051
Hello, I have a bit of a situation, and I think I know the answer but this font of knowledge may prove something. I want to do the unthinkable...
Replies
6
Views
2,242
Back
Top Bottom