OT- Connecting transformers "backwards"

katratzi

Member
Join Date
Mar 2005
Posts
210
Is it "code" or legal to connect a transformer in reverse?
We have 6kva 460 to 230 volt three phase transformer. A customer has 208 volt three phase at his facility. He has a machine that
requires 400 volt 3 kva. This works out well because a 208 volt input on the secondary side will produce close to a 400 volt output on the primary. If it is fused correctly, is it o.k. to do this?

I have heard from some that this is not a good idea, that small kva units are usually built with a two winding "T" connection
(whatever that is) and should not be run backwards. What do you guys think?
 
The only problem is that the efficiency of the transformer does go down. Since your transformer is rated 2x what is required, it should not cause problems. Make sure the output voltage does not rise too high. I have seen and done many secondary input and primary output transformer connections.
 
katratzi said:
Is it "code" or legal to connect a transformer in reverse?
We have 6kva 460 to 230 volt three phase transformer. A customer has 208 volt three phase at his facility. He has a machine that
requires 400 volt 3 kva. This works out well because a 208 volt input on the secondary side will produce close to a 400 volt output on the primary. If it is fused correctly, is it o.k. to do this?

I have heard from some that this is not a good idea, that small kva units are usually built with a two winding "T" connection
(whatever that is) and should not be run backwards. What do you guys think?

A T-connected transformer only has two coils rather than the normal 3 coils. These units often have extra windings on the high voltage/primary side in order to compensate for the internal losses (primarily due to the magnetic flux). Running Tee units backwards would mean that the output voltage would not be 480V and it will have poor voltage regulation.
 
Jim Dungar said:
A T-connected transformer only has two coils rather than the normal 3 coils. These units often have extra windings on the high voltage/primary side in order to compensate for the internal losses (primarily due to the magnetic flux). Running Tee units backwards would mean that the output voltage would not be 480V and it will have poor voltage regulation.

In this case I do not see a problem, the T winding may actually work in your favor since the input will be 208v the output may be closer to the 400v you desire then 416v. That and the fact the power rating is twice what you need.
 
sorry, Jim. you must have posted while I was typing!
how much voltage deviation are we talking about? the power draw
is minimal.
 
katratzi said:
sorry, Jim. you must have posted while I was typing!
how much voltage deviation are we talking about? the power draw
is minimal.

I don't think you can predict the deviation. This may not be a problem, but it is something you need to be aware of.
 
Is a T type transformer the same as an "auto transformer" ? In other words there is only one coil with a separate taps for the "primary" and "secondary" (*).
As far as I remember, these would only be used when there is a small difference between primary and secondary voltages (i.e 180V/230V). I think that 208V/400V is a strangely high ratio for an auto transformer.
Apart from that, using it for either step-up or step-down should mean no difference. Only, it must be rated for the highest voltage of course.

*: Edit. One coil per phase.
 
Last edited:

Similar Topics

Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
29
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
81
Hello, I was looking to store some values from our FactoryTalk Application using Datalog to a MariaDB. I see there is quite a bit of documentation...
Replies
1
Views
88
I haven't encountered problems connecting to a PLC through VM Ware but I am with this particular machine. I'm running Windows 7 on a Windows 10...
Replies
8
Views
229
Hi, I want to build a demo station to test devices and programs and I need some help with it. I want to connect GuardLogix, Piltzmulti and...
Replies
1
Views
149
Back
Top Bottom