<No Devices> with Versa View 1250H

JohnU

Member
Join Date
Apr 2007
Location
Cable, Wi
Posts
1
Hello: I have a new out of the box Versa View 1250H terminal. I am trying to connect this to a DH485 network and SLC 5/03. In RSLInx I can see my laptop and SLC but not the Versa View terminal.

On the terminal when I select terminal Settings | Networks and Communications | RSLinx enterprise communications I see Virtual backplane, Ethernet, and Serial-DF1. However, all of these show <No Devices>. Hence I am unable to configure the node number of the terminal as described in the manual. I have cabled the terminal to my SLC network via the DH485 connector.

I also have a Panel View 600 that exhibits the same problem so I suppose I am doing the same thing wrong there as well.

Any ideas?

Thanks.
 
Well, DF1 is RS232 so that's why it won't see the PV+ or PV.

In RSView ME, go into "RSLinx Enterprise" - "Communications Setup."
Once there, right click on the "RS Linx Enterprise, COMPUTER NAME" and then add a driver for RS-485. That may get you started.

On the PV600... may be something similar. There, you are going to have to have a copy of RSLinx Classic and configure the RS-485 driver in that. If you're trying to get your laptop to talk to the PV for screen transfers, then RSLinx Lite (the one that comes with RSLogix500) should be ok.

Anyway, play around with the RS-485 drivers and see if that helps. It probably will. Eventually <g>.
 

Similar Topics

Hi, I am looking for some help with a GE Fanuc Versa Max Micro Controller model IC200UDR001-BF connected to a Quickpanel mini display...
Replies
3
Views
145
anyone know how to turn off the touch screen beep on a versa view 6300 with an eGalaxTouch screen, windows 10:mddr:
Replies
4
Views
1,655
I have 5 systems that include a ControlLogix PLC and a Micrologix 1400 PLC. I need to connect these two via ethernet. I want to have two inputs on...
Replies
1
Views
1,778
Good Day, I am hoping someone can help me. I saw from some earlier posts that you converted a Versa Pro program to a pdf file for another...
Replies
4
Views
1,691
When I want to store the hwc file to the PLC an error apears and said the firmware 5.03 is incompatible with versapro, and the minimum version...
Replies
9
Views
3,163
Back
Top Bottom