Hi,

I have two racks in configuration and TSX 57203 CPU in the First Rack.

When i connect my laptop the CPu cannot sense the second rack modules.

between the racks the connecting cable is connected.
In the HArdware configuration it is howing red for both the racks.
but i can access the first rack .

unable to access the modules in secon rack .

Do anybdy knows what could be the reason.

Best Regards
Dheeraj
 
Make sure the terminator is installed at the far end of the last backplane. And make sure your BusX cables are properly connected.
 
thx for the reply.

actually the racks have the dip switches which i didn't set.
others the bus x cables are connected properly

On setting the dip switches the rack is being sensed.
 

Similar Topics

Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
107
Hello All, I'm currently having issues getting a backup rack for a Modicon Premium TSX H5744M to function properly when it is brought online...
Replies
0
Views
1,145
I'm working on a project and have found myself in a situation where I need to use a PCMCIA card (I think a TSX SCP 114) to read modbus registers...
Replies
6
Views
1,787
I am experiencing a very strange problem. I have purchased tsxcusb485+tsxcrjmd25 cable in order to communicate with a Modicon Premium TSXP57103...
Replies
2
Views
4,228
Hi ALL, We have a Modicon TSX Premium PLC-Processor TSX PSY1610, which has a "Low Battey Fault" and cannot run I am searching for the software...
Replies
6
Views
2,586
Back
Top Bottom